    Wire size & conduit size for 60 am subpanel 150 from source
    Indiana question:
    I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement.
    What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run.
    John
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Nov 22, 2008, 08:41 AM
    John,

    Good morning. This site is set up for DIY users doing residential work. Not commercial installations.

    Please contact several licensed electricians and get bids.

    For example, if this were a residence, then you would use a #4/3 AWG copper with a 70 Amp breaker (sized for continuous use), 240/120 single phase connection.

    However, I believe that Commercial uses three phase not single phase.
    maguyver's Avatar
    maguyver Posts: 7, Reputation: 1
    New Member
     
    #3

    Nov 23, 2008, 01:14 AM
    6 gauge
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Nov 23, 2008, 05:52 AM
    jmavris, if you have to come to a DIY message board to ask this question than obviously you are not qualified to do this work in a commercial environment.
    Are you licensed to do this work? Obviously not. :mad:
    Are you insured to do electrical work?? :rolleyes:

    CALL AN ELECTRICAL CONTRACTOR to do this work, the a$$ you save could be your own.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Nov 23, 2008, 07:12 AM
    Where is this requirement or limitation stated in this website?:

    Quote Originally Posted by donf View Post
    This site is set up for DIY users doing residential work. Not commercial installations.
    While usually single family dwellings can be done by a homeowner, and everything beyond a this must be done by a qualified tradesman, I do not see why any question about anything other than a residential application is not allowed.

    Please provide backup for your statement.

    This is incorrect:

    Quote Originally Posted by donf View Post
    For example, if this were a residence, then you would use a #4/3 AWG copper with a 70 Amp breaker (sized for continuous use), 240/120 single phase connection.
    Per NEC 2008 edition Table 310.15 (B) 6 - #4 copper can be used for a 100 amp residential feeder.


    This statement illustrates some lack of knowledge and experience in the trade:

    Quote Originally Posted by donf View Post
    However, I believe that Commercial uses three phase not single phase.
    Various two pole single phase electrical equipment, to include circuit breakers, panelboards, and disconnects are made up to 1200 amps single phase, and certainly are not limited to residential applications.

    In an effort to answer the original question, while #6 copper is the minimum size conductor allowed for a 60 amp feeder, consideration must be taken for the load and distance. If the max load is 48 amps at 120 volts, the max wire size to allow for no more than 3 % voltage drop would be #3 copper wire.

    This is a design issue, not a code issue, and a qualified electrician and/or engineer needs to be consulted to size this feeder.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Nov 23, 2008, 09:53 AM
    The answer, "This is for DIY residential" comes from past history on this forum.


    I based my sizing on 240/120 vac, 150' length, continuous use (60 X 1.25% = 75 amp). Since the breaker will be carrying a constant load to the second building.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    Nov 23, 2008, 09:57 AM
    Question, when sizing conductors for a 240/120 vac run, does the 120 vac take precedence over the 240 vac for calculation purposes?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #8

    Nov 23, 2008, 02:08 PM
    The 120 or 240v have NO bearing on wire size.

    The only time they do is in figuring voltage drop, and we won't get into that now. TK and I strongly disagree on that subject. :p ;)
    mohdbg's Avatar
    mohdbg Posts: 2, Reputation: 1
    New Member
     
    #9

    Jul 12, 2010, 02:36 AM
    You can use 4c*16sq.mm cu /xlpe/swa cable in 50 mm dia.conduit with one pull box at 30 m.
    Hope this will answer yor question.
    Regards
    Mohd
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #10

    Jul 12, 2010, 04:02 AM

    Mohd, it is safe to say the OP is in North America and you are not, so your advice is not accurate for the situation.

    Also, this thread is almost two years old. Please check the dates of the posts you are replying to.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire & underground conduit size [ 1 Answers ]

Hi, I will need an electrical wire run between a small transformer and the main control panel for the house. I expect the transformer to push 220 or 240 volts at 200 amps. The transformer will be just under 140 feet from the panel. What size wire should I use and what is the minimum size...

Wire Size 60A Subpanel [ 1 Answers ]

I am finishing up a bathroom addition and need to add a subpanel next to the existing 200A main panel to clean-up several 'doubled-up circuits I found in the main panel as well as provide breakers for the new bathroom installation. I plan to install a 100A sub-panel within a foot of the...

Proper wire and conduit size? [ 2 Answers ]

Hi, I have just had a new pole building built. I had a 200 amp service installed. I will be installing 16 fluorescent light units. I will install them on at least 2, possibly 3 circuits. My question is what is the formula for figuring out the proper wire size, and how many of these conductors can I...


View more questions Search