    Lennox G20 2a fuse on circuit board blows
    The 2a fast blow fuse blows immediately on this G20e. Can not tell from schematic what the cause might be. Anybody have this problem before. What part or parts need to be replaced? Cost of parts? (this is the fuse on the circuit board that is visible when the fron covers are off the furnace).
    esquire1's Avatar
    esquire1 Posts: 2,483, Reputation: 209
    Ultra Member
     
    #2

    Sep 21, 2008, 09:40 AM
    You have a short in the low voltage circuit. Most the times with this problem I find that something (dog or weedeater) has cut the 2 small wire coming from the inside airhandler to the outdoor conding unit or that the contactor coil is bad
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #3

    Sep 21, 2008, 10:00 AM

    Try disconnecting all the thermostat wires from the printed circuit board , these are the wires that go to the thermostat and outside unit, put a new fuse in and try it, if it does not blow the fuse then reconnect one wire at a time to determine which one causes the fuse to blow. This will point you in the direction of the problem such as a shorted wire, burnt contactor coil or relay, good luck, Mike
    lennoxquestion's Avatar
    lennoxquestion Posts: 6, Reputation: 1
    New Member
     
    #4

    Sep 21, 2008, 10:59 AM
    Quote Originally Posted by esquire1 View Post
    You have a short in the low voltage circuit. Most the times with this problem I find that something (dog or weedeater) has cut the 2 small wire coming from the inside airhandler to the outdoor conding unit or that the contactor coil is bad
    ESQ1, thanks for reply. I have no outdoor unit, no central air. Furnace only.
    lennoxquestion's Avatar
    lennoxquestion Posts: 6, Reputation: 1
    New Member
     
    #5

    Sep 21, 2008, 11:07 AM
    Quote Originally Posted by acetc View Post
    Try disconnecting all the thermostat wires from the printed circuit board , these are the wires that go to the thermostat and outside unit, put a new fuse in and try it, if it does not blow the fuse then reconnect one wire at a time to determine which one causes the fuse to blow. This will point you in the direction of the problem such as a shorted wire, burnt contactor coil or relay, good luck, Mike
    Thanks for the reply Ace. You and ESQ1 both mention contactor coil, where is this located? Also, what relay are we talking about? Is the relay on that circuit board? BTW, this unit is at my 3 season cottage 200 miles away, and I won't be getting back there for at least a week to check on your suggestions. Really appreciate the hellp/info ;))
    esquire1's Avatar
    esquire1 Posts: 2,483, Reputation: 209
    Ultra Member
     
    #6

    Sep 21, 2008, 11:58 AM
    If heating only, still is a low voltage. Check wires from the thermostat to the furnace. Make sure no wires are totching in the stat. You haven't be working inside the thermostat have you? Could be a mouse hase chewed insulation off wires
    lennoxquestion's Avatar
    lennoxquestion Posts: 6, Reputation: 1
    New Member
     
    #7

    Sep 22, 2008, 06:05 AM

    Thank you, will check on this and post back in about a week.
    lennoxquestion's Avatar
    lennoxquestion Posts: 6, Reputation: 1
    New Member
     
    #8

    Oct 2, 2008, 09:36 AM

    I used the G20 troubleshooting flowchart and identified the problem as the BCC circuit board. This is on order and will be replaced. Will update when I kow for sure if this fixed the issue.
    lennoxquestion's Avatar
    lennoxquestion Posts: 6, Reputation: 1
    New Member
     
    #9

    Oct 13, 2008, 07:03 AM
    Ok, I checked the thermostat and there is nothing wrong with it. I replaced the BCC2 circuit board with the latest level, a BCC3 card, and the furnace fired right up. If anyone has any problems with the Lennox furnace, I advise using the troubleshooting flowchart and a multimeter and the problem should be found. FYI, the BCC2 card cost about $120 plus shipping. I purchaased mine online through hvacpartsshop.com and the service was flawless.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Turning on AC blows control board fuse and 24v transformer [ 15 Answers ]

I read https://www.askmehelpdesk.com/heating-air-conditioning/c-keeps-blowing-fuse-95884.html which was very informative. My issue is with a Carrier Weathermaster 8000 furnace and York AC. The heat works fine, the fan only works fine, I turn on the AC and the LED blinks code 34. I replace the...

My Lux aire control board fuse blows. [ 1 Answers ]

I have a heat pump systems a LuxAire made by York it is ony 4 year old the model number is: F2FP048H06G I have isolate all t/stat wire in and tested for possible grownding with negative result. I did rung the A/H fan on on and works find but when I set the unit for cooling or heating it blows...

ICM271 Carrier Replacement board Fuse blows [ 4 Answers ]

My Furnace recently stopped working and the Furnace Fan stayed on constantly. I replaced the original Fan Control circuit board (HH84AA011) with a ICM271 drop in replacement board. Still nothing came on, not even the constant fan. I check the 120V-24V transformer and found no 24V output so I...

Turning on A/C blows 3amp fuse on circuit board [ 1 Answers ]

Hi, Hope someone can help me. As stated in the title, when ever I turn the a/c on it blows the 3 amp fuse on the board. The system works fine with heat on. It's only when I activate the a/c does it burn. I have no idea what is causing the fuse to blow. Does anyone have any ideas of where I can...

Goodman controller board fuse blows [ 8 Answers ]

I have a Goodman GMPN120-5, service guy replaced PCB in Aug due to A/C failure, root cause unkknown or not documented. Last week I turned on heat for first time this season, now nothing runs. Service guy returned, located blown 3A PCB fuse, replaced, still blows. Replaced fuse with 5A for testing...


View more questions Search