    Quote Originally Posted by massplumber2008
    Hi MK...

    The picture posted actually shows that the utility sink has no vent at all. For a vent to be a sink vent it must come off ABOVE the ptrap of a the sink. Clearly there is no vent coming off the top of the trap so this is an unvented fixture and should be fixed now if you have the chance....(just so you know anyway). You could install an individual vent as required and connect to other vents or you could also install a provent (see picture #1) here if not going to be inspected, but at least the provent would allow air to mix as utility sink drains AND allow air to enter into the system when water flows through that pipe to the left instead of pulling it from the trap of the utility sink and siphoning the ptrap dry and allowing sewer gasses into your home when the fixture (kitchen sink perhaps??) above drains (a health hazard)...so if get chance, at a minimum consider the pro vent (see picture #2)....*whew*...;)

    OK...now what is this about using the sanishower system for the shower and the sink?? Great system...but why can't you get all this to gravity drain...?? Let me know more...ok??


    Chat soon...MARK
    So that's why the sucking sound always... however the traps remain wet, the sink was that way when we moved in and has always been that way I suppose...

    But, the reason I can get this to all gravity drain is because the shower base is raised already about 8" which is the max because my shower doors are 72... the way I had to connect the san t to the existing clean out has caused me to have more height that expected... I'm already going to have to raise the floor an additional 3.5 to 4 inches because of this and the mimnium drop caused by the elbow to toilet flange, unless you know of something else

    But as of now this is how I plan on connecting to the stack,




    Its too high to allow me to run all of the shower piping and sink piping with a downslope of even a 1/8th inch. And I have this as tight as I can get it...

    Unless I can put a 45 ele at the stack run a wye then a 45 from the toilet, other side of wye I could install a T with a clean out? And then connect piping from shower and sink??

    Let me know what you think of this,

    However no inspections so if wetventing isn't to code but will work fine lets do that... if this works what I just had... wow that was a revelation
    mechanickid's Avatar
    mechanickid Posts: 248, Reputation: 5
    Full Member
     
    #22

    Aug 29, 2008, 02:24 PM
    OK... I've done it

    Pictures are ready... atfirst I found this on the right and started freaking out, but soon took off the clean out cap and realized this wasn't the path I could see...



    Is that an old clay pipe?? Didn't think the house was that old and the basement seams to have a consistent cement... anyway

    Here is a eye level of the pipes... if this continues on this path... it will intersect closly with the shower drain and sink.








    If you need to see more let me know

    I want the toilet to be in this area... to the right of the overall view picture... but within the hole I opened up so far.
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #23

    Aug 29, 2008, 03:28 PM
    Hi Brian... excellent job! I see you don't mess around!

    The clay pipe is an inside perimeter drain pipe so try not to disturb this too much.. ok (I would have you cover the clay pipe with some gravel and then a liner fabric before closing up the hole... can discuss later).

    I'll draw up the best way to pipe this up a little later tonight. I am going to present the piping in the wet vent manner discussed earlier.

    You really lucked out with the pipe headed as it is... and not too deep. Seems you have a little luck on your side.. ;)

    See if you can locate some lennox diamond sawzall blades at your area home depot or similar. If they don't have diamond blades then the carbide blades do OK, too.

    Ideally a local plumbing supply house will be open tomorrow morning and you can go purchase the correct fittings and clamps. If not, then we can come up with another solution... best overall will be to get a cast iron no-hub wye fitting and some no hub or mission style clamps. Check local supplier in the AM and I'll give you a list for them if they are open. If not, then I'll give you another list to go to home depot and get supplies there... I am thinking you can finish this up this weekend and get working above ground next week!

    PS: That looks like it is 4" cast iron underground...a good thing!! Just so you know!

    Talk soon...

    MARK
    mechanickid's Avatar
    mechanickid Posts: 248, Reputation: 5
    Full Member
     
    #24

    Aug 29, 2008, 03:56 PM
    Quote Originally Posted by massplumber2008
    Hi Brian...excellent job!! I see you don't mess around!

    The clay pipe is an inside perimeter drain pipe so try not to disturb this too much..ok (I would have you cover the clay pipe with a some gravel and then a liner fabric before closing up the hole...can discuss later).

    I'll draw up the best way to pipe this up a little later tonight. I am going to present the piping in the wet vent manner discussed earlier.

    You really lucked out with the pipe headed as it is....and not too deep. Seems you have a little luck on your side..;)

    See if you can locate some lennox diamond sawzall blades at your area home depot or similar. If they don't have diamond blades then the carbide blades do ok, too.

    Ideally a local plumbing supply house will be open tomorrow morning and you can go purchase the correct fittings and clamps. If not, then we can come up with another solution...best overall will be to get a cast iron no-hub wye fitting and some no hub or mission style clamps. Check local supplier in the AM and I'll give you a list for them if they are open. If not, then I'll give you another list to go to home depot and get supplies there...I am thinking you can finish this up this weekend and get working above ground next week!!

    Talk soon...

    MARK

    soundss great mark... I know that the one main plumbing supply in my area is closed sat and Monday because of labor day, but of course home depot is open, however there could be another local plumbing supply open, not sure though
    there is a local hardware store it's a True Value, but this place is huge and has been here forever, they cary everything, alota people say if you can't find it anywhere check northside, and usulay they do have it. This place will be open,

    haha, and no I never mess around, I'm the kind of guy that will work his off until its done then take a break and if I'm talking about it I will problay want to do within ten min, don't like to mess around,, as you can see,
    sometimes this works sometimes it gets me into a mess, haha



    question, since I see that your still here, if this runs in the directon of the shower drain should I just do two sepret cuts? Or should we stay with one?

    oh and the perimnter drain... it had a small amount of gravel, but some dirt fell down in that crack? Is that OK? Should I be concerned?

    this is the stack above my floor and underneath the first floor.




    the cast iron wye goes to second floor full bathroom, the galvanized steel pipe is from first floor shower/bath and then the pvc is from the first floor toilet

    if possible could we use the open 2inch fitting for the venting? Only things above this is the firstfloor sinks, there are two small ones


    thanks
    -Brian
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #25

    Aug 29, 2008, 07:25 PM
    Hi Brian...

    No issue with a little dirt getting into the clay pipe... happens at every joint between clay sections. Just be sure to cover with 3/4" to 1" gravel stone.

    Sorry... that 2" tapping is a waste line tapping and will not be anything close to a vent for this bathroom. I bet if you chase out the other 2" tapping with galvanized piping that it picks up the lavatory or tub..? Let me know.

    As presented... YOU WON'T LIKE THIS... but we will need to get a little creative with the venting to this bathroom, but we discussed fact that venting was going to be tough underground or above the floor so that really is not a change as much as a fact.

    I mentioned connecting in at least 6 inches above the sink in the bathroom... either you need to connect into the stack a foot or so above the sink on 1st floor or you will need to run vent into the attic and connect vent from this bathroom up there (or could go with accessible PRO-VENT.. but since going this route I suggest you go full tilt and finish accorrding to code and tie 2" vent into vent system as described! ). We will discuss more.

    Anyway.. I will draw up some basics... be right back... (refresh screen every 5 minutes until you see next post).

    MARK
    mechanickid's Avatar
    mechanickid Posts: 248, Reputation: 5
    Full Member
     
    #26

    Aug 29, 2008, 07:32 PM
    Haha, OK on standby refreshing every 5 min, don't rush though I'm in my own world... however, I did label all of those connections in my post. The galv pipe goes to the tub on first floor yes

    For venting... kind of worried about this... don't have any access to the vent stack between here and the attic, even in the attic I was looking its really cramped not much space at all... what about, I've read about air valve... I forget what its called, the alztimers is kicking in again
    mechanickid's Avatar
    mechanickid Posts: 248, Reputation: 5
    Full Member
     
    #27

    Aug 29, 2008, 07:34 PM
    Ahhh... air admittance valve
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #28

    Aug 29, 2008, 07:45 PM
    A start...

    Refresh again in 5 minutes. Hoping I did not confuse files... BRB

    Ahhh.. AAVs... yes.. may be option in this case... we'll see. First is to present best choice... work from there... ;)
    Attached Images
      
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #29

    Aug 29, 2008, 07:49 PM
    Hi Brian... get that floor opened a bit more and dig down so the dirt is under pipe.

    I will post all info needed from here by 8:00am eastern time... check back then.

    I am having fun with this and think you are doing a great job. Talk in AM... my little guy wants to play!

    MARK
    mechanickid's Avatar
    mechanickid Posts: 248, Reputation: 5
    Full Member
     
    #30

    Aug 29, 2008, 07:51 PM
    Quote Originally Posted by massplumber2008
    a start...

    Refresh again in 5 minutes. Hoping I did not confuse files...BRB

    Ahhh..AAVs...yes..may be option in this case...we'll see. First is to present best choice...work from there...;)

    Haha OK, No Files are looking good, keep in mind... I'm no longer at the job, so I can not take any additional pictures tonight, I may have some saved in email I can look if you need others.

    ? Question? ->am I using iron for anthing other than the wye?
    mechanickid's Avatar
    mechanickid Posts: 248, Reputation: 5
    Full Member
     
    #31

    Aug 29, 2008, 07:53 PM
    Quote Originally Posted by massplumber2008
    Hi Brian...get that floor opened a bit more and dig down so the dirt is under pipe.

    I will post all info needed from here by 8:00am eastern time...check back then.

    I am having fun with this and think you are doing a great job. Talk in AM...my little guy wants to play!!

    MARK

    OK good good,, go go

    I have a little one also, a new one for me :) talk soon thanks, I'm hoping for a early start so as early as you can, but don't get up any eariler...


    Thank you
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #32

    Aug 29, 2008, 07:55 PM
    No.. after wye I hoped to transition to pvc via an adapter or clamp.

    And missed one question. You should take this off the one 4"x3"wye I drew earlier... not two fittings.. will explain in AM.

    Good night...

    MARK
    mechanickid's Avatar
    mechanickid Posts: 248, Reputation: 5
    Full Member
     
    #33

    Aug 29, 2008, 07:58 PM
    Quote Originally Posted by massplumber2008
    No..after wye I hoped to transition to pvc via an adapter or clamp.

    And missed one question. You should take this off the one 4"x3"wye I drew earlier...not two fittings..will explain in AM.

    Good night...

    MARK

    Goodnight

    Thanks
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #34

    Aug 30, 2008, 04:26 AM
    OK.. here is some more info.:

    see next post for more info.



    .
    Attached Images
      
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #35

    Aug 30, 2008, 04:44 AM
    OK...

    You will need to purchase:

    1-4"x3" no-hub cast iron wye fitting
    2-4" 4-band clamps (best here..see 1st pic.) or can purchase shielded clamp (2nd pic.), but don't buy fernco rubber clamps (third pic.).

    1-3" shielded clamp that transitions from cast iron to pvc plastic pipe (will say so on the clamp)

    PVC cement
    Pvc primer
    2-3" 45 degree fitting
    2-3" street 45 degree fitting
    1-3" pvc 90 degree fitting
    10 feet 3" pvc pipe
    1-3"x2" pvc wye
    1-2" pvc wye
    2-2" pvc couplings
    1-2" pvc ptrap without cleanout
    3-2" pvc 45 degree fittings
    3-2" pvc street 45
    1-2" dandy cleanout (also called a test tee... see fitting picture)
    2-2" pvc 22.5 degree fittings
    2-2" pvc street 22.5 degree fittings
    1-2"x1.5" sanitary tee fitting (will be installed above ground to pick up sink)
    10 feet 1.5" pvc pipe
    3-1.5" pvc couplings
    1-1.5" pvc 90 degree elbow
    2-2" rubber jim caps (see last pic... cap pipes after they come out of ground)
    1 can rectorseal pipe dope (for lots of things as we go along).
    1-3" jim cap (toilet)
    20 feet 2" pvc pipe

    That should get you started. If can't find the 4x3 no-hub cast iron wye then will need to purchase a 4"x3"PVC wye, a 10 foot piece of 4" pipe and 2-4" no-hub x 4"pvc adapters....ok?? You will still use the original clamps.

    I have included a few extra fittings...JUST IN CASE! You may want to purchase other fittings as well... they can be returned.


    Some basics here:

    All pipes pitch at 1/4" pitch per foot.

    Toilet pipe gets roughed in so it is 11.5" to 12" to center of pipe from rear finished wall.

    Sink gets piped so it centered on sink. Sink pipe ends up at 18" to center off the finished floor... so if traveling 4 feet from the vertical 2" pipe you must start the 2" pipe you must start the 2" sanitary tee at 17" to center from finish floor so ends up at 18" off finish floor in the end.

    Shower p-trap placement cannot be finalized until you have the shower base in home... so for now can stub to shower area and cap for now and then get the shower, determine correct rough in and then will place the shower p-trap.

    We can discuss testing all this once you get all this piped and capped.

    For now, stub the 2" sanitary tee at 17" and cap (after cementing over floor you will add the 2" dandy cleanout here and then the 2" pipe out of ground about 20" sanitary tee for the sink).

    Obviously, after the wall is built by the sink you can drill through the studs and install the sink waste.

    No regular 90s underground... only long sweep 90s... can make using 45 and street 45 fittings as I discussed with you earlier.

    Let me know if you have questions. You know my number... ;)

    MARK
    Attached Images
         
    mechanickid's Avatar
    mechanickid Posts: 248, Reputation: 5
    Full Member
     
    #36

    Aug 30, 2008, 05:24 AM
    Quote Originally Posted by massplumber2008
    OK...

    You will need to purchase:
    Let me know if you have questions. You know my number...;)

    MARK

    Hey mark...

    Thanks for all this,

    One question? When I attach the iron wye, do I make the part that comes off sloped a little bit?( if you were to put a level on the piece perpendicular it would not be level across it, so the part leading to the toilet is sloped into the drain pipe slightly?)
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #37

    Aug 30, 2008, 05:34 AM
    Hi..

    Yes you want to install so has pitch up.

    When get set to cut into the cast iron you would lay the fitting on top of the pipe and then cut the pipe so it is about 3/4" longer than the fitting....this is very important..ok?? This 3/4" excess will allow for the clamps inner rib.

    You will install the clamps, slide clamps back, then bend the rubber parts back upon themselves, then install fitting, then flip rubbers back to grab the fitting.. then slide clamps in place and clamp this up to a proper torque.

    Keep me posted
    mechanickid's Avatar
    mechanickid Posts: 248, Reputation: 5
    Full Member
     
    #38

    Aug 30, 2008, 05:40 AM
    Ok got it,, thanks

    Going shoping now and plan to be cutting by 11

    Thanks so much Mark
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #39

    Aug 30, 2008, 05:42 AM
    Good luck!. don't forget to add sawzall blades to your list!!
    mechanickid's Avatar
    mechanickid Posts: 248, Reputation: 5
    Full Member
     
    #40

    Aug 30, 2008, 05:52 AM
    You still here?

    Can't find the CI WYE could you explain the route I have to take to install the 4" wye?

    Oh and I do have the shower already :)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to fix basment wall leaks [ 2 Answers ]

I have water coming into my basment through the walls. Mainly where the wall meets the floor. How can I take care of this problem.

Basment not level [ 3 Answers ]

Hi... Just bought a house and the basement is not level. What can be done to create a level floor ready for carpeting. How much with labour and material would it cost?

Leaking basment [ 3 Answers ]

I have a old house with a stone foundation, what's the best way to seal a stone foundation, we are getting leaks from a couple areas. Thank you Rob

New bathroom in basment [ 2 Answers ]

Hello I have a couple of questions, first off I am building a bathroom in my basement. It is a new house only 2 years old there are two stubs in the basement. One is the small one which I am guessing is the toilet the other a large square hole filled in with rock. I am guessing this is for the tub....

Too hot upstairs too cold in the basment! [ 2 Answers ]

I'm trying to fix a problem in my house. There is only one thermostat and it is on the main floor but heat rises! So upstairs is really hot! In the basement it's really cold! What is the best way to fix this? I am renovating the basement so I would like to fix this before I cover the ducts up. I...


View more questions Search