    Honeywell RTH230B
    I am installing a Honeywell RTH230B thermostat but am not sure of the wiring. I have 6 wires colored as follows, red, green, white, yellow, and 2 blue wires.

    Please advise?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Mar 12, 2006, 11:20 AM
    You will need to check the heating system and identify the function of the blue wires. If one isn't connected, likely the other is the common, C. If you have a heat pump, the second blue wire may be part of switching modes. Otherwise follow the standard connections.

    Usually there is a 24 volt AC transformer in the furnace with the secondary winding connected to a red wire running to the thermostat and a blue wire, common, to the gas valve, A/C relay, and fan relay. From the thermostat there will be white wire to the gas valve, yellow to the A/C, and green to the fan. The thermostat is wired to switch the power from the red to the white, yellow, and green as needed with the blue completing the circuit. Most thermostats and furnaces have the contacts labeled R, B or C, W, Y, and G for the corresponding wire colors. It may be wired to have the A/C control wires return to the furnace and its controls and then a second wire goes to the A/C unit. Internal wiring may replace the green wire if the thermostat does not give you the option of fan only or continuous fan. Digital or programmable thermostats may need the blue wire connected to them.

    Jumper the red wire to RC and RH. If you do a search, you will find the RTH230B a troublesome unit I haven't been very successful with helping people. Some people have found they need to change batteries and select the correct operation. I hope you have the directions in English. There are people here that can give much better advice than this in some other areas. I am doing what I can here until somebody better comes along.
    Bmartin's Avatar
    Bmartin Posts: 10, Reputation: 1
    New Member
     
    #3

    Mar 12, 2006, 11:47 AM
    Thanks... I'll have a look... If it helps, I'm replacing a RobertShaw 9420.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Mar 12, 2006, 01:08 PM
    Did you note what the blue wires were connected to if anything before?
    Bmartin's Avatar
    Bmartin Posts: 10, Reputation: 1
    New Member
     
    #5

    Mar 13, 2006, 05:20 AM
    The labels are Y2, Y1, E, W2, G, O, B... iin addition to L, C, R... The connections were:

    Red- R
    Blue- C
    Yellow- Y1
    Green- G
    White- W2
    Blue- B

    The problem is the RobertShaw thermostat was working perfectly until about a month ago, then it started clicking off altogether (no reading or anything) and would be "dead" for about a day or two then come back alive.

    It would only come back alive after I've had the switch turned off for a few hours, (sometimes 24 or more).
    Bison's Avatar
    Bison Posts: 3, Reputation: 1
    New Member
     
    #6

    Apr 15, 2006, 10:36 PM
    Just a note about the Honeywell RTH230B (It appears this thermostat has some notoriety around here). I recently replaced and installed this thermostat from a non-programmable Honeywell I had. My HVAC system is as follows: gas fired furnace with an outdoor A/C unit. The existing wiring was five wires routed from a low voltage panel (located in the indoor gas fired furnace) to the new thermostat like below:
    Rh - red wire
    Rc - Blue wire
    W - White wire
    Y - Yellow wire
    G - Green wire

    So, each wire I connected to an independent connection on the back of the new prog thermostat. In addition, from the outdoor A/C unit, I have two wires routed to the low voltage panel in the furnace. They share connections with wires from the tstat on the "C" & "Y" connection on the low voltage panel.

    This setup worked great (for the heating season, anyway) until the cooling season arrived today. This made sense to me at the time - 5 wires, 5 points of connection. Done, right. Little did I know.

    My girlfriend came to me this morning and said she had turned the tstat to cool, but the outdoor unit nor the indoor blower engaged. So, I started my investigation.

    Turns out even though I have 5 wires from the low voltage panel routed up to my thermostat, the Blue (Rc) wire, however, was not to be used from the low voltage panel (through trial and error and lot of reading today) . Instead, I placed a jumper connection between the "Rh" and the "Rc" connection at the tstat and kept the red wire hooked up (at the "Rh" connection), along with the remaining 3 wires (this is a 4-wire configuration). I based this on the manual from the Honeywell RTH230B thermostat. You may know there are various methods (5-wire , 4-wire etc) for connection.

    Now, my cooling system works fine and my heating does too.

    I hope this may help someone in the future, because I know by reading here today helped me a great deal too.

    Just want to share.

    Thanks,
    B
    jss27560's Avatar
    jss27560 Posts: 1, Reputation: 1
    New Member
     
    #7

    Apr 16, 2006, 12:26 PM
    I seem to be having a similar problem. The house is a dual zone system and the upstairs is working fine. The down stares is where the problem is. It is also where the RHT230B is installed. The heat worked fine but switching to the AC doesn't. I seem to bet getting air blowing thought the vents but it doesn't seem cool. There are 4 wires going to the tstat and they are connected to the corresponding spots on the tstat.

    The outside unit is a Trane 'Gas Pack'. Not sure what exactly a gas pack is unless it is another name for the heater/AC unit. I tried moving the jumper from HE to HJ but it seems to only cause the air to blow harder from the vents. But when I checked the tstat it the blower has stopped.

    The house is a rental so I don't know everything about the heating/cooling system. I know there is something in the attic but I'm unable to check it right now.

    I'm going to call the landlord tomorrow and have then take a look at it tomorrow but it's 80 deg down stares and that is hot.

    Jeff

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Honeywell RTH230B [ 3 Answers ]

I currently have a very old thermostat, White-Rodgers 135-415, which I'd like to convert to a Honeywell RTH230B. Currently there are only 3 wires that are connected to the thermostat (which is only for my apartment's heat. White wire is connected to what looks to be labeled "Common" Black...

Honeywell rth230b [ 4 Answers ]

This winter I installed honeywell rth230b. Heater works great, but I have no a/c. I have 6 wires from wall. Rh--red Rc--blue W--white Y--yellow G--green Brown not being used Help it is 90 deg. I need my a/c Thank you all

Honeywell rth230b thermostat [ 3 Answers ]

We hooked up the honeywell programmable thermostat and it was working fine for 10 days or so until this weekend when the temperature should be at 67 all day from 6am to 10pm and 62 from 10pm until 6am on sat and sun. this weekend the thermostat does not bring the temp up to 67 but it leaves it at...

Honeywell RTH230B Thermostat [ 1 Answers ]

I recently installed Honeywell #RTH230B thermostat to replace and old Honeywell # T87F( old round non digitital type). I have oil burner with basebaord water heat. Since my olf thermostat was 2 wire only and I have no AC I pulled the jumper wire between Rh and Rc as per the instructions. Thj9is...

Honeywell Thermostat RTH230B [ 14 Answers ]

I have 6 wires to connect. The colors are as follows: W, Y, G, B, O, and R. The thermostat calls for W, G, Y, Rc, and Rh. Where do I plug in the R and what do I do with the B and O? Any help would be greatly appreciated. Thank you