    No pressure in heating boiler
    One of heating pipes bursted.
    Replaced pipe and all is sealed.
    Gauge indicates no pressure temp reads 180
    Disconnected pressure regulator and water comes out strong on outlet end.
    Have heat circulating on most of the first floor.
    No heat circulating to second floor.
    Water feed is feed, pressure regulator, expansion tank with y fiiting, y fitting to air purge w
    A air vent attached on top, t into boiler tank and main house feed.
    Why is there no preesure and what to check?
    Thank you
    therinnaiguy's Avatar
    therinnaiguy Posts: 153, Reputation: 5
    Junior Member
     
    #2

    Jan 23, 2008, 05:16 PM
    If you have zero pressure indicated by the gage, your auto-feeder is not working. Look for a small regulator on the cold water intake pipe coming from your domestic water supply to the boiler. Most auto-feeders look like an upside down ice cream cone with a small tail on top. Lift this tail, you should hear water entering into the system. Carefully watch your pressure gage to make sure it is rising. Do not put more than 20 pounds of water into the system otherwise the relief valve will spit out boiler water. Most likely you will need to purge the air out of your second floor zone. Once your system is up to pressure, get a technician in to replace the auto-feeder and purge your system.
    askmealice's Avatar
    askmealice Posts: 8, Reputation: 1
    New Member
     
    #3

    Jan 23, 2008, 06:03 PM
    Is auto feeder same as pressure regulator
    It is a WATTS #3156 (an upside down cone with a lever on top
    Lifted lever and hear no water entering system and still no pressure
    therinnaiguy's Avatar
    therinnaiguy Posts: 153, Reputation: 5
    Junior Member
     
    #4

    Jan 25, 2008, 07:16 AM
    Make sure all valves are open upstream to the Watts. If so, you need to replace the feeder.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Dunkirk boiler fired baseboard heating unit. [ 1 Answers ]

Burner won't light up with pilot on.Could it be the filter?Where filter is located?

Combi boiler: Hot water but no heating [ 3 Answers ]

Hi, Our boiler has started to act up on us. I had the heating on constant the other day. I was up in the bathroom and heard a strange sound coming from the boiler. I ran the hot tap to wash my hands and the water spurted out and it was brown in colour. The boiler had locked out. I tried...

Hammering in my hot water heating boiler [ 1 Answers ]

I have a zoned in floor hot water heating system that is hammering. The system hammers in the boiler when I have only one zone on. When more than one zone calls for heat, then there is no hammering. * I have installed spiro vents to remove all of the air. * I have checked the pump, and it is...


View more questions Search