    1 out of 3 heating zones not working
    Our heating system seems to be operational... specially given the fact that 2 out of the three zones work like a charm.

    The zone that doesn't work uses a "Honeywell V8043 E 1012 motorized valve", and since the problem started, we've replaced the motor only... and it didn't work. Now, we've replaced the entire valve, and we still have the same issue. In addition, if we set the valve to ON (instead of AUTO), the heating will work, but it'll warm up too much as there's no governor to tell it to stop heating.

    We've also switched thermostats from the zones that work to the non-working one, and no deal.

    Can someone please give us some ideas of what to look into to better troubleshoot and determine the root cause for our problem?. as I'm writing this, it's making me believe that the wiring from the 2nd floor (problem zone) to the basement may be at fault... hope that's not the case. Anyway, any insight will be greatly appreciated.

    Thanks,
    Gus W.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 23, 2007, 08:13 AM
    You might have nailed the problem but before you jump to replacing the wires check the valve and wires out.
    Check to see if there is a signal source/24 volts going to the valve motor.
    Next check the end switch operation if the valve has a end switch.
    Next tie the 2 wires for the end switch together (jump wiring) this is supposed to send a signal to the boiler to start up or start the pump. See what happens.

    Report back with your findings.

    A diagram for you.

    http://customer.honeywell.com/techli.../95C-10932.pdf
    gusw's Avatar
    gusw Posts: 3, Reputation: 1
    New Member
     
    #3

    Dec 23, 2007, 10:57 AM
    Thanks for all the info. We'll check and let you know how it all worked out.
    gusw's Avatar
    gusw Posts: 3, Reputation: 1
    New Member
     
    #4

    Dec 24, 2007, 07:41 AM
    Thank you again. After all, it was the wire from the valve to the thermostat in the 2nd floor that was the problem. The information you provided was very helpful, nonetheless, in narrowing down the problem.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Lynnox Heating System not working properly [ 5 Answers ]

Hi, My 7 yrs old Lennox Elite Series heating system is having a problem. While the thermostat setting is set to 70 degree, the furnace is not shutting off. Rather, it keeps heating the house to the low 80s. If I turn the thermostat off, the furnace will shut off too. Can you help?

New two zone heating system not working. [ 1 Answers ]

We are about to close on a new condo and we had a two zone system put in. The problem is when the heat is off upstairs and the temp is set around 70 in the lower level the temp in the upper level reaches 74 or higher and you can feel the heat coming out the vents. The contractor says this is...

Heating and hot water not working [ 1 Answers ]

Hi We have a relatively new boiler (I think - we moved into the house 6 months ago) and it has suddenly stopped heating. It makes all the right noises but I don't get any heating in the central heating system or any hot water. Can someone help?


View more questions Search