    adidasprof's Avatar
    adidasprof Posts: 2, Reputation: 1
    New Member
     
    #1

    Dec 16, 2005, 04:16 PM
    Heat won't stop running
    I just moved into a new house, well new to me. It has a heat pump system. I'm not familiar with them at all and need some help. I took out my old mechanical thermostat and replaced it with a programmable digital thermostat. Now my problem is that the heat won't quit running. I don't know if I have it wired incorrectly or not. From my old thermostat (Lennox 21J7201) the wires were tied in like this
    R=Red
    Y1=Yellow
    G=Green
    0=Orange
    C=Blue
    W1+E=White

    The white was tied in to both the W1 and the E. In the new thermostat (Hunter model # 44260) the wires are tied in like this:

    G=Green
    RH=Red also has jumper to RC from factory
    Y/O=Orange
    W/B=White
    Y1=Yellow

    Do I just have the wrong type of thermostat? I don't know if I have a single stage or multistage heat pump. Any help would be greatly appreciated.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Dec 16, 2005, 05:44 PM
    Red, R, RC, and RH are all power from the transformer. White, W and W1 should be the signal for heat. Yellow, Y1 is the signal for cooling. Green, G is for fan only. Blue, C is the common from the transformer. Orange, O usually connects to the reversing valves on a heat pump. E may have been meant for a different heating rate and jumpered to W to call for a single rate of heating when the thermostat signaled for either rate of heat. Only Hunter knows what Y/O and W/B do. You are going to have to pick through the instructions and figure out what they do, and then connect the proper wire to them. See what you can find. Post back. If you haven't fixed it, maybe you will have found enough out somebody else here or I can figure it out.
    adidasprof's Avatar
    adidasprof Posts: 2, Reputation: 1
    New Member
     
    #3

    Dec 16, 2005, 05:53 PM
    Thanks Labman,

    According to the instructions:
    RH, R, VR, or 4= RH 24 Volt
    RC, VC= RC 24 Volt
    G, F = Fan
    Y/O = the reversing valve operation in cool mode
    W/B = the reversing valve operating in heat mode
    Y1 = Heat Pump Compressor
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Dec 16, 2005, 08:39 PM
    From those instructions I would assume the thermostat switches power to W/B when ever the heating mode is selected, and then to Y1 when it calls for heat. I think you want to connect the wire that goes out to the heat pump compressor, yellow? to Y1 on the thermostat, and the wire that goes to select the heat position for the reversing valves to W/B. If the reversing valves only seems to have one pair of wires, try connecting both its hot wire and the hot wire to the compressor Y1, and nothing to W/B or Y/O.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Changing from gas heat to electric heat [ 3 Answers ]

How do you change from Apollo gas heating system to electric heating system?

Running furnace fan without heat [ 5 Answers ]

I read some of the other similar posts. I am encouraged that there is a way to do without a spot for the green wire. Labman, could you give me directions on how you to accomplish this. Thanks so much! Nate

Heater won't stop running [ 3 Answers ]

I have a Frifidaire central heating & air conditioning system 2 years old. Today we set thermostat to cool and the heater continues to run and will not shut off by thermostat control. Pulled the thermostat and heat continues to run. Currently off as I switched off the breaker at the outside unit....

Tractor won't STOP running... [ 1 Answers ]

I purchased my tractor 4 months ago. Today as I was mowing my yard, when I wanted to stop, the brake would not engage and the tractor kept moving. When I tried to re-start the tractor, although the tractor was in park, the tractor began to move again. Any suggestion as to the cause or diagnosis to...

Water won't stop running [ 3 Answers ]

Changed the stems and the cold water works fine but I can not get the hot water to stop running. I have the handle turned off completely and it runs like I have it wide open. Please help us as soon as possible


View more questions Search