    Why won't my infloor heating system circulate through the system?
    I am having infloor heating circulation problems, My pump is running and the water at the pump is hot but it is not running through the rest of the piping. What would cause the water not to circulate?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 25, 2007, 11:03 AM
    Air in the system. Weak pump impeller.
    ymeski56's Avatar
    ymeski56 Posts: 5, Reputation: 1
    New Member
     
    #3

    May 17, 2008, 08:11 PM
    Yep, distance between chamber surface & impeller surface no longer within operational tolerance. Happen to all centrifugal pumps sooner or latter depending multiple usage variables.but you should have noticed decreased performance long before this point.Based on the limited and insufficient amount of info provided suggests you don't intend to fix it yourself. You just want to be able to call bull with confidence if your repair tech tries to turn a service call with 20 min.s in labor to adjust the pump if his good hand is in a cast, into a big dog and pony show.If pressure loss occurred abruptly it is more likely the pump intake supply line is restricted by an inline strainer and/or prefilter.(very popular pump warrany requirements).simple and easy to rectify.If this is the case continued use of pump will case motor damage($$$$) If its pump cavitation ,continued use will also require seal replacement and will continue to leak past the seals till replaced (less w/ pump off -more w/ pump on. Shut down system, call service tech. Ask him to explain how it functions,how to do the general maintenance & how you can monitor your system for proper operating performance. Hope this helps you. I'd like to here about how it went from here!
    therinnaiguy's Avatar
    therinnaiguy Posts: 153, Reputation: 5
    Junior Member
     
    #4

    May 19, 2008, 08:07 AM
    Quote Originally Posted by ymeski56
    Yep, distance between chamber surface & impeller surface no longer within operational tolerance. happen to all centrifugal pumps sooner or latter depending multiple usage variables.but you should have noticed decreased performance long before this point.Based on the limited and insufficient amount of info provided suggests you don"t intend to fix it yourself. You just want to be able to call bull with confidence if your repair tech tries to turn a service call with 20 min.s in labor to adjust the pump if his good hand is in a cast, into a big dog and pony show.If pressure loss occurred abruptly it is more likely the pump intake supply line is restricted by an inline strainer and/or prefilter.(very popular pump warrany requirements).simple and easy to rectify.If this is the case continued use of pump will case motor damage($$$$) If its pump cavitation ,continued use will also require seal replacement and will continue to leak past the seals till replaced (less w/ pump off -more w/ pump on. Shut down system, call service tech. Ask him to explain how it functions,how to do the general maintainence & how you can monitor your system for proper operating performance. Hope this helps you. I'd like to here about how it went from here!
    Simply Stated!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heating system isn't heating.. Is there a pilot that needs lighting? [ 1 Answers ]

I am renting a home that is 50 years old. It has recently turn cool, low 30s. If I turn the heating/air switch to heat and 70 + degrees. All I get is cool air coming out of the air vents. Can someone tell me what things I should do before calling heating specialist?

Heating system [ 1 Answers ]

How do I stop my furnace from building up 15 lbs. of pressure (steam boiler, radiators), and having my pressure releif valve open and filling my cellar with lots of steam.

Heating system [ 1 Answers ]

1. What would cause my copper hotwater pipes to blacken with a sooty powder? We removed a wall during remodeling and found the pipes with a black sooty powder. It comes off on to your hand when touched. Plus, we found a plug with blackened cooper also..? Any help would be appreciated. 2....


View more questions Search