    Parallel Thermostats
    I Am installing baseboard electric heat in 2 rooms in my basement on a new
    20 amp 240v circuit. In the first room I'm putting 1 1500 watt heater and 1
    1250 watt heater for a total of approx 11.5 amps (connected parallel).
    My question is this:
    Can I run a parallel connection from the first thermostat to another thermostat in the other room and then install a 1000 watt heater to the 2nd thermostat? (total amps for the baseboard heaters in the 2 rooms would be approx 16 amps.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Dec 1, 2005, 07:02 AM
    If you are asking if you can run a cable from the line side of the thermostat to the second thermostat, no problem. That is commonly done as long as the feeds go to the thermostats an d then to the heaters.
    dherman1's Avatar
    dherman1 Posts: 129, Reputation: 10
    Junior Member
     
    #3

    Dec 1, 2005, 10:58 AM
    Related Electric Baseboard Heat question
    Howdy,

    A year ago I converted my attic into a craft room for my wife.

    Although, I am not sure I would call a 30' long, 12' wide room with through the wall A/C, DirectTV with TIVO, wireless LAN access, 3 Skylights, etc a "Craft" room but, then again, she is in the Scrapbooking Cult. <grin>

    Since we live in Minnesota, she also wants it to be heated. Go Figure!

    And herein lies my question.

    I am installing 2 Electric Baseboard heaters. They are 240V on a 20amp circuit. Thinking that I would need 12-3 with ground I ran a new circuit up from the basement, under the floor and then into a box to connect to the Stat. It turns out that all I needed was 12-2. So, what do I do with the Red wire? The Black and White connect to the double pole breaker and the ground to the ground.

    Should I cut and cap off the Red wire and leave it in the main panel or would it be better to do that to the White wire?

    Thanks in advance for your help.

    Dan
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Dec 1, 2005, 02:15 PM
    I would cap off the white. Don't think it makes much difference.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Physics (Current and Parallel Forces) [ 3 Answers ]

Hi HelpDesk: Please I need help how to figure out these problems: 1) An auto engine of mass 295Kg is located 1.0 m from one end of a 4.0 M work-bench. If the uniform bench has a mass of 45.0Kg, what weight Must each end of the bench support? 2) There is a graphic like:

Slopes,parallel and perpendicular... how do I do that?help please! [ 2 Answers ]

okay I was given the linear equation 2x+4y=12 and I was asked to find: a.)an equation in the form y=mx+b b.)an equation of line parallel to the equation c.)a slope perpendicular to the equation d.)an equation of a line parallel & through the point (4,2) e.)an equation of a line perpendicular...

Thermostats HELP [ 2 Answers ]

Okay guys I just moved into a new place and the thermostat is way off. It's a mechanical one, so today I went out and bought a honeywell programmable one and tried to install it. The problem is the wiring which I have no clue. What is included in the honey well is: Y G W Rc Rh

Two Thermostats to One [ 2 Answers ]

I currently have a separate thermostat for the heater and the A/C... I want to combine them into one thermostat... I have replaced the thermostat before, but my knowledge of the wiring is very basic... My issue is that I have two "R" wires and I am worried about combining them together since it is...

Can I use parallel thermostats in a 1-zone system? [ 3 Answers ]

Bought an old 3-storey house in Maine, heated with gas forced-hotwater radiators. There is only 1 zone, with the thermostat in a 1st floor front room with little traffic and away from any radiator. When the t'stat calls for heat, it takes so long for it to register at the t'stat site, that the...


View more questions Search