    We need to run some 12/2 Romex through the floor joists of a newly built home. Can we drill the floor joists wherever we see fit, or are there limits?
    Evelyn11's Avatar
    Evelyn11 Posts: 5, Reputation: 1
    New Member
     
    #2

    Nov 7, 2005, 06:20 AM
    I should have been a bit more clear with my question. My concern, and the disagreement with the SO, is where along the length of the joist can we drill? Does it need to be in the outer thirds of the span, leaving the middle span untouched?
    RickJ's Avatar
    RickJ Posts: 7,762, Reputation: 864
    Uber Member
     
    #3

    Nov 7, 2005, 06:56 AM
    Now that you say that, I recall hearing it before.

    In checking it out, I see that the "rule of thumb" is actually to go through the middle third.

    After finding this article, the next 3 I found confirmed the same thing:

    When possible, drill through the joist with the smallest bit necessary to allow passage of the pipe or wire. Confine the drilling to the center line of the center third of the board
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Nov 7, 2005, 07:39 AM
    There are some requirements on spacing the wires too. Searching tkrussel's posts in electrical and lighting may turn them up. If you don't find them, post the question there. Nobody here gives better answers on electrical stuff.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Nov 7, 2005, 06:04 PM
    I am surprised by the website rickj found, which states the wiring must be confined through the center third of the span of joist. This is not how it is done in the real world.

    Unfortunately , I do not have a BOCA or IBC, building codes handy to be able to quote exactly the code article or section. I can tell you as being in the indusrty over 30 years, the recommended location of drilling any hole in the center third is just not done, or allowed.

    The National Electric Code does not address this issue, only building codes, due to structural integrity of the framing members.

    NEC only addresses the location of a hole from the edge of a member, must be at least 1-1/4" away from the top or bottom edge, to prevent a nail or screw from being driven into the wiring.

    Think about it... as I believe you have realized.. the center of any span of a framing member is the area of weakest, where there will be the greatest bending and flexing. Any hole in this location shall compromise the strength.

    Imagine drilling holes only in the center third of a bridge, where the strength must be the greatest to counter act the down ward forces of weight being loaded on it. I will be swimming across the river before I wlak across that bridge.

    We are not allowed to drill holes for any wiring in the center third of a floor joist, all holes for wiring must be in either or both of the outer thirds of a span, as you seem to already be aware of.

    Since the actual codes are not available on the internet, I have only been able to find various forums to back my claim.

    Since you are wiring your new home, you should be applying for a permit to wire, and you can certainly check me with your local electrical and/or building inspector.
    Evelyn11's Avatar
    Evelyn11 Posts: 5, Reputation: 1
    New Member
     
    #6

    Nov 7, 2005, 06:18 PM
    Thanks
    Thanks for your replies.

    I told Dan to run it down the side- but no... He should use his own name to post, doncha think?

    Anyway: Drilling a 1/2 inch hole in any part of the span- given using the vertical, top to bottom center third is OK as long as you do not notch a joist in any part of the center third (horizontally). We asked the Bldg Inspector about the 1/2 inch hole. I doubt it would ever be acceptable to drill a large hole in the center center. Notching is right out.

    I know it is confusing- but it does make sense to avoid the horizontally measured center third of the span as a general rule.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Nov 7, 2005, 06:41 PM
    If I understand you correctly, your inspector said to drill your holes in the center, right? Then there you go, hope you got that in writing, or by his acceptance of the installation is approval of this method.

    I will not be drilling holes in the center third of the span ,measured horizontally, however.

    Driling a hole in the center of the vertical is fine, as I stated the NEC only limits you to 1-1/4" from the top and bottom edges.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #8

    Nov 7, 2005, 07:14 PM
    Didn't you post some rules for how far a hole needs to be from the next wire?
    BuilderDan's Avatar
    BuilderDan Posts: 1, Reputation: 1
    New Member
     
    #9

    Nov 8, 2005, 05:36 AM
    OK, so I wasn't registered and used my wife's name to post. So sue me.

    The interesting thing is that when I Googled "drilling a floor joist" one of the forums said to limit the holes to the center third, and leave the last foot at either end alone.

    I don't know what we'll have to do if the inspector decides to be a jerk and say we can't do it after it has been done. Replace the joist?
    Borewyrm's Avatar
    Borewyrm Posts: 65, Reputation: 2
    Junior Member
     
    #10

    Jan 8, 2006, 11:41 AM
    Well what it comes down to is "What your inspector says."

    Now the other problem with this question is what type of lumber are you talking about? Main beams are often built using Microlams. Other joists may be normal 2x4 material or engineered TJI beams. The manufactuarer specs can be found by contacting them. But they are all different. We work in various municipalities and the rules vary based on both location and the inspector (Yes the inspoector can't make his own rules, but its bad to argue unless pressed). In one place for example the microlams may only be drilled once! That's one hole not to be in the middle third of a span. So if the plumber gets there first we need to run wires roundabout.
    mad5077dm's Avatar
    mad5077dm Posts: 1, Reputation: 1
    New Member
     
    #11

    Apr 1, 2006, 03:43 PM
    You should follow manufacturer specs when drilling any manufactured beam or laminate product. Typical joists should be drilled in the center 1/3. Someone made the comment that this isn't the real world. As a licensed home inspector I come across many of the "real world" situations. There is a right way and a wrong way. It may take a little more time and money to do it right. That is why many builders and subs take short cuts and someone else has to pay to redo the job the right way. And just because it gets by the "code" inspector doesn't mean that it was done correctly. The code inspectors are usually overworked and underpaid and have many sites to visit and only so much time to do it. They can't see everything.
    oldmanspoon's Avatar
    oldmanspoon Posts: 1, Reputation: 1
    New Member
     
    #12

    Jun 28, 2006, 07:23 PM
    The 2003 International Residential Code covers this:
    Not exceeding 8 feet (2438 mm).
    R502.8Drilling and notching. Structural floor members shall
    Not be cut, bored or notched in excess of the limitations speci-
    Fied in this section. See Figure R502.8.
    R502.8.1 Sawn lumber. Notches in solid lumber joists, raf-
    Ters and beams shall not exceed one-sixth of the depth of the
    Member, shall not be longer than one-third of the depth of the
    Member and shall not be located in the middle one-third of
    The span. Notches at the ends of teres shall not exceed
    One-fourth the depth of the member. The tension side of
    Members 4 inches (102 mm) or greater in nominal thickness
    Shall not be notched except at the ends of the members. The
    Diameter of holes bored or cut into member shall not exceed
    One-third the depth of the member. Holes shall not be closer
    Than 2 inches (51 mm) to the top or into member the member, or
    To any other hole located in the member.Where the member
    Is also notched, the hole shall not be closer than 2 inches (51
    Mm) to the notch.
    R502.8.2 Engineered wood products. Cuts, notches and
    Holes bored in trusses, laminated veneer lumber, glue-laminated-
    Members or I-joists are not permitted unless the effects
    Of such penetrations are specifically considered in the design
    Of the member.
    R602.6Drilling and notching—studs.Any stud in laminated members
    Wall or bearing partition may be cut or notched to a depth not
    Exceeding 25 percent of its width. Studs in non bearing parti-
    Tions may be notched to a depth not to exceed 40 percent of a
    Single stud width. Any stud may be bored or drilled, provided
    That the diameter of the resulting hole is no greater than 40 per-
    Cent of the stud width, the edge of the hole is no closer than 5/8
    Inch (15.9 mm) to the edge of the stud, and the hole is not lo-
    Cated in the same section as a cut or notch. See Figures
    R602.6(1) and R602.6(2).
    Exceptions:
    1. A stud may be bored to a diameter not exceeding 60
    Percent of its width, provided that such studs located
    In exterior walls or bearing partitions are doubled and
    That not more than two successive studs are bored.
    2. Approved stud shoes may be used when installed in
    Accordance with the manufacturer’s recommenda-
    Tion.
    R602.6.1 Drilling and notching of top plate.When piping
    Or ductwork is placed in or partly in an exterior wall or interior-
    Or load-bearing wall, necessitating cutting, drilling or notch-
    Ing of the top plate by more than 50 percent of its width, a
    Galvanized metal tie of not less than 0.054 inches thick
    (1.37mm) (16ga) and 11/2 inches (38mm) wide shall be fas-
    Tened to each plate across and to each side of the opening
    With not less than eight 16d nails at each side or equivalent.
    See Figure R602.6.1.
    Exception:When the entire side of the wall with the notch
    Or cut is covered by wood structural panel sheathing.

    R802.7 Cutting and notching. Structural roof members shall
    Not be cut, bored or notched in excess of the limitations speci-
    Fied in this section.
    R802.7.1 Sawn lumber. Notches in solid lumber joists, raf-
    Ters and beams shall not exceed one-sixth of the depth of the
    Member, shall not be longer than one-third of the depth of the
    Member and shall not be located in the middle one-third of
    The span. Notches at the ends of the member shall not exceed
    One-fourth the depth of the member. The tension side of members 4 inches (102 mm) or greater in nominal thickness
    Shall not be notched except at the ends of the members. The
    Diameter of the holes bored or cut into members shall not ex-
    Ceed one-third the depth of the member. Holes shall not be
    Closer than 2 inches (51mm)to the top or bottom of the member-
    , or to any other hole located in the member. Where the
    Member is also notched, the hole shall not be closer than 2
    Inches (51 mm) to the notch.
    Exception: Notches on cantilevered portions of rafters
    Are permitted provided the dimension of the remaining
    Portion of the rafter is not less than 4-inch nominal (102
    Mm) and the length of the cantilever does not exceed 24
    Inches (610 mm).
    R802.7.2 Engineered wood products. Cuts, notches and
    Holes bored in laminated veneer lumber, glue-laminated
    Members or I-joists are not permitted unless the effect of
    Such penetrations are specifically considered in the design of
    The member.
    R802.10.4 Alterations to trusses. Truss members shall not
    Be cut, notched, drilled, spliced or otherwise altered in any
    Way without the approval of a registered design professional.
    Alterations resulting in the addition of load (e.g. HVAC
    Equipment, water heater) that exceeds the design load for the
    Truss shall not be permitted without verification that the truss
    Is capable of supporting such additional loading.
    bhayne's Avatar
    bhayne Posts: 339, Reputation: 4
    Full Member
     
    #13

    Sep 1, 2006, 11:57 AM
    Drilling joists to run wiring. A clear code violation. What is the inspector thinking?
    Run the 12/2 down the joist to the wall and along the wall. If not you should install some EMT along the bottom of the floor joist to run the 12/2. 12/2 indicates an outside supply so you may want to run it in PVC instead.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #14

    Sep 1, 2006, 01:08 PM
    Can you provide that actual code Article and Section that states that drilling wood framing members is not allowed?
    bhayne's Avatar
    bhayne Posts: 339, Reputation: 4
    Full Member
     
    #15

    Sep 1, 2006, 01:21 PM
    Sorry, I should be saying, "what was I thinking". Cables of any size may be run through bored holes in joists in unfinished basements.
    law1234's Avatar
    law1234 Posts: 1, Reputation: 1
    New Member
     
    #16

    Feb 2, 2008, 11:52 PM
    THis should answer everything you need to know
    Notching a Joist | Framing | How-to | This Old House
    daisy27's Avatar
    daisy27 Posts: 33, Reputation: 2
    Junior Member
     
    #17

    Feb 5, 2008, 05:37 PM
    Quote Originally Posted by Evelyn11
    We need to run some 12/2 Romex through the floor joists of a newly built home. Can we drill the floor joists wherever we see fit, or are there limits?
    Yes you can .but you can not drill the upper third or lowwer third!
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #18

    Feb 5, 2008, 05:58 PM
    Law and Daisy, did either of you notice this post is 2 years old?
    saratogans's Avatar
    saratogans Posts: 4, Reputation: 1
    New Member
     
    #19

    Feb 7, 2008, 08:48 AM
    Quote Originally Posted by Evelyn11
    We need to run some 12/2 Romex through the floor joists of a newly built home. Can we drill the floor joists wherever we see fit, or are there limits?
    1st you need to check with local building inspection dept for your jurisdiction. There are specific limits - and for good reason: you are potentially changing the structural integrity of the lumber. It may even be listed on line if the local community has uploaded their codes. Do not just follow someone else advise. Find out what is appropriate and permitted for your community.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #20

    Feb 7, 2008, 11:44 AM
    Saratogans, Law and Daisy, did any of you notice this post is 2 years old?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Joist thinkness for installing a toilet? [ 3 Answers ]

I'm thinking about installing a toilet in an upstairs that has 2 x 6" joists. Will there be room for closet bend in the floor? Thanks

Oil Drilling? A few questions? [ 1 Answers ]

My class is doing our own debate about drilling oil in antartica and we need statistics and facts to help our debate. I am on the team that is againts drilling and I'm curious how drilling pil would affect animals. Can someone tell me?:)


View more questions Search