    Calibrating clamp temp probe?
    I have a UEI Multi meter and use a pipe clamp type temp sensor for Superheat and Subcooling... How can I make sure it is accurate? Would it be internal on my Electric meter or on the Clamp? I can't seem to find any info. I know reg temp sensor ice water would be good for 32*. Can I get the clamp type probe into ice water? Any help would be great. Thanks, brian
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Oct 9, 2007, 10:56 PM
    If I filled a bathtub with ice and water, I'm sure your pipe clamp would fit. <G> Here is how to make an ice bath for calibration: Thermometer and Temperature Calibration Using a Triple Point of Water

    Normally you would use two pints to calibrate. Boiling water and ice.

    The sensor type would help.
    Stubby74's Avatar
    Stubby74 Posts: 34, Reputation: 4
    Junior Member
     
    #3

    Oct 10, 2007, 03:08 AM
    Thanks for response... my concern for putting clamp probe in ice water was if it would short out.? I know suction lines are wet... but putting completely in water was the issue... and if off... how to adjust? Thanks.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Oct 10, 2007, 03:33 AM
    You want to know about the clamp probe and you ae using a UEI multi-meter. We could care less about the UEI multi-meter. I'd like to know about the clamp probe. Make, model and what sensor it's based on and the temperature limits.

    Are there any electronics associated with the probe? Does it require batteries? What do you select on the multi-meter. All are clues.
    Stubby74's Avatar
    Stubby74 Posts: 34, Reputation: 4
    Junior Member
     
    #5

    Oct 10, 2007, 04:17 PM
    K simple... Cooper Atkins Type K clamp probe... model 4005mk. No batteries, just plugs into multi meter... put probe to Temp setting.. and boom.. reading... just unsure how accurate it is and best/ easiest way to either test or calibrate! Thanks
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #6

    Oct 10, 2007, 04:26 PM
    The clamp type is made to check surface temp but if you open it up with out clamping it down to anything it will sense air temp check it against a different probe that just senses air temp.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #7

    Oct 10, 2007, 06:33 PM
    Now we are getting somewhere. K type thermocouples are usually accurate to at least 1 degree and they are good to 1200 deg. C. The wire is made up of a junction of two dissimilar metals, do there is not much that can go wrong. When making the junctions, you can inadvertently create too many twists, but that's not likely in commercial manufacturer. Limits of error is at least +-1 degree.

    The measuring instrument now is the limting factor. If you short the input with a wire, the measuring instrument will read room temperature.

    You need a calibrator to assess the accuracy. One such calibrator is here. Type K Thermometer/Calibrator, 800010

    The distilled water ice bath and the distilled water boiling water if done properly should find any gross errors. You need a two point calibration. It's best to do it near the temperatures of interest.
    tsa7man's Avatar
    tsa7man Posts: 154, Reputation: 9
    Junior Member
     
    #8

    Oct 15, 2007, 06:42 PM
    Take a 6 inch or so... piece of 3/4 copper pipe and put it in your freezer for a few hours. Take it out and immediately clamp on your temp probe... it everything is set your meter will read 32 degrees...
    Stubby74's Avatar
    Stubby74 Posts: 34, Reputation: 4
    Junior Member
     
    #9

    Oct 16, 2007, 03:01 AM
    Thanks for all your help. Brian

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Calibrating an Airguide auto compass [ 8 Answers ]

I have an Airguide compass for my car but have lost the instructions. How do you set it up. It is the basic model with suction cups and a round globe on a square base

Differential of return temp and cooled exit air temp [ 1 Answers ]

Here is the problem I am having, I had a new unit installed last year on my new house. I noticed that the compressor runs for a long time and shut off for a short period. This got my attention and wondered if the unit is running efficiently. I had my doubts from the start since the A coil looked...

Temp gauge showing temp, 2001 Chev Malibu [ 13 Answers ]

I have a 2001 Chev Malibu LS, V6, temp gauge is not showing any heat at all, not registering when I know the coolant is hot ? Veh has about 126000 mi on it, never been flushed out, thought I would attempt to flush myself but don't you think the problem might be a bad thermostat ? If so, where and...

Need flange clamp for old toilet [ 2 Answers ]

I've got an old raised-tank toilet in the basement of a house I just bought. The bowl was clamped to the drain line coming up from the floor by a wire 2-piece clamp that tightened with 4 nuts. The clamp was totally rusted and one of the bolts broke off when I bumped it. I took a picture of the...

Question about supply temp. & return temp. [ 3 Answers ]

The AC system produced supply temps. At 57-60 degrees on the first floor With a return temp. of 71 degrees. The second floor supply temp. is at 59 degrees with a return temp. of 72 degrees. I know there should be at least a 15 degree temp. difference from the supply to return. There was also an...


View more questions Search