    Powering the G terminal on my furnace control board
    Hi! My furnace's control board recently blew and the repair guy replaced it with a different kind. Aparently the new board requires a wire from the thermostat to the G terminal to work the A/C fan, and the old one didn't. The repair guy would need to make another trip for this repair.

    I am wondering if I could fix this myself. Since replacing the wire to the thermostat would be a big job (the wire is stapled and runs a long long way behind walls and under floors) I hope to fix it without a new wire.

    - Can I add a jumper in the furnace from the Y terminal to the G terminal? Y seems to be used to turn on the A/C, so it seems to make sense to power G whenever Y is powered. Is this safe?

    - Lots of schematics I found show that the C terminal wire is optional. Can I move that wire from the furnace and thermostat C terminals to the G terminals? What does C do? All I can determine is that is possibly powers the thermostat? Why is it optional then?

    - Why does the fan turn on fine when heat is called for when there is no G wire?

    Thanks for any insights :)
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Oct 6, 2005, 08:10 PM
    OK, thermostat wiring 101:

    Usually there is a 24 volt AC transformer in the furnace with the secondary winding connected to a red wire running to the thermostat and a blue wire, common, to the gas valve, A/C relay, and fan relay. From the thermostat there will be white wire to the gas valve, yellow to the A/C, and green to the fan. The thermostat is wired to switch the power from the red to the white, yellow, and green as needed with the blue completing the circuit. Most thermostats and furnaces have the contacts labeled R, B or C, W, Y, and G for the corresponding wire colors. It may be wired to have the A/C control wires return to the furnace and its controls and then a second wire goes to the A/C unit. Internal wiring may replace the green wire if the thermostat does not give you the option of fan only or continuous fan. Digital or programmable thermostats may need the blue wire connected to them.

    I think in some systems the signal for the blower is connected on the board. In other systems, the thermostat powers both the yellow and green wires. If you jumper the Y and G at the board, the A/C will come on if you select fan only at the thermostat. If you seldom use the fan only setting, not much loss. If the thermostat can be set to power the G terminal when calling for air, and you have an unused blue wire and no green, you could use it in place of the green.

    The white wire usually supplies power on the board to the blower relay, often a different relay for a slower speed coil in the motor. Thus, the blower runs with the heat.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bad Furnace Control Board? [ 6 Answers ]

I have a Carrier 58PAV that intermittently aborts or sometimes clicks on and off at the draft blower stage. I found out I can move the control board (HK42FZ007) when the blower motor clicks off, and it clicks and comes right back on. If I hold it just right, the furnace starts and if I manage to...

Power to furnace control board but stops there [ 3 Answers ]

Hi I was given a Nordyne KG6RA gas furnace. After installing, I turned on and there was a low hum when the power got to it. I held the door switch closed so I could see. After a few seconds there was a spark and then blue smoke and everything went dead. I could not see where the smoke came...

Wiring question for new blower control board [ 1 Answers ]

Just bought the Lennox blower control board replacement kit - 31M73 I'm stuck on wiring the transformer--- The five wires coming out of the transformer going to the old board are - Yellow - common Blue - 24 vac Orange-L2 XFMER Primary Black - L1 XFMER Primary Red - PARK

No RC terminal on new thermostat? [ 8 Answers ]

Hello: I saw your name on an internet search for thermostat wiring problems, so I thought I would try you for this one. I could not get help elsewhere. I have an oil burner, and a separate a/c unit. I installed a programmable thermostat 2 years ago that works well, although the location is...


View more questions Search