    Central Air Conditioning Watts
    How many watts are in a typical 3 ton central A/C unit, 5 ton unit and 10 unit? Does
    Anyone know? I'm trying to figure out how much of my electricity bill is due to air conditioning and heating cost.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Aug 30, 2007, 04:04 PM
    First you would have to figure your consumption of electric by the appliance. How many hours the unit has run and how many amps it takes it to run for one hour. Once you have those figures you can just use a amp to watts converter available on Google search.
    caibuadday's Avatar
    caibuadday Posts: 460, Reputation: 10
    Full Member
     
    #3

    Aug 30, 2007, 04:34 PM
    Quote Originally Posted by ken1972
    How many watts are in a typical 3 ton central A/C unit, 5 ton unit and 10 unit? Does
    anyone know? I'm trying to figure out how much of my electricity bill is due to air conditioning and heating cost.
    You can't really tell, some like temp of about 72 but others like80, of course at72 it would cost more than 80, and it also depened on the outdoor temp... I think the best way is let it run for about 5 min then take ampere, conversen it into watt then muptiply with the time it run( most stat now have run or filter time recording), and add that to the evap fan
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Aug 30, 2007, 04:51 PM
    You can estimate based on the data sheets.

    An example:

    2-1/2 Ton 208/230 Volt 1-Phase Scroll Compressor Direct Factory Replacement Part (Copeland): American HVAC Parts

    is a 2.5 ton compressor at 2.5 HP
    You can assume a 1/3 HP outside blower and a 1/2 HP inside blower.
    2.5 + 1/3 + 1/2 =3.33 HP
    Add about 25 W for controls

    Running watts would be about 746*3.33 + 25 that 2486.8 W
    Call it 2.5KW; there are 746 W/HP

    At $0.15/KWH it's about 2.5 KW * $0.15/KWH = $0.375/hr to operate

    If it runs 5 hours per day 5 * 0.375 * 30 = $31.75/month

    Hopefully, my math is right. Running time could be off. Each month could be different because it depends on the cooling degree-days

    Once you find a fudge-factor for degree-days, you might be able to get a seasonal cost.

    USATODAY.com

    Look at the nameplate for similar information.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Aug 30, 2007, 05:15 PM
    Consider another answer:

    One ton of refrigeration will equal approximately 3517 watts, so a 3 ton unit will draw 10551 watts. This is the load that is used to size service entrance calculations.

    Assume the unit runs 5 out of 24 hours a day for one month:

    150 hours x 10551 watts = 1582650/1000 = 1583 KWH @ $0.15/KWH = $237.45 per month.

    Plug in your cost of a kilowatt-hour and the hours per day the unit runs and go from there. Should be close.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Aug 30, 2007, 06:11 PM
    There are a lot of good answers here but the only way I found to satisfy my commercial customers years ago was to use a chart type recorder and calculate the exact amount of draw and at what temperature. For the average person buying these type of devices would be cost prohibitive. That is why I did not mention it in my first post. A/C equiptment draws a different amount of power depending upon how efficient it is and how hard it has to work to keep up with the outside temperature. On a cool day the a A/C unit might draw 20 amps but of a 100 degree day it might draw 22 amps. The condenser discharge temperature will be higher as the outside temperatures go up. The compressor has a harder time compressing the return gas into a higher pressure gas which in turn becomes a liquid in the condenser coils to start the cycle over by going back to the evaporator as a liquid to flash once again to a gas to pick up more work load from the inside of the home.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Central air conditioning problem [ 2 Answers ]

My central air conditioning unit seems to work well with normal air flow. On several occasions at night the inside coil has frozen allowing little air to pass. I have reset the thermostat to a higher setting allowing the coil to thaw and air flow returns to normal. The daytime temps have been in...

Central air conditioning unit auto shut off does not kick in [ 3 Answers ]

Our central air conditioner would not start. Since we had this covered under our utility provider's WorryFree Services program, they sent a technician to look into the problem. The technician had to replace something like a transformer which had died due to old age. The airconditioner runs now...

Central Heat and Air not blowing air at all [ 1 Answers ]

Hello, I am a girl trying to save myself a little money and maybe embarrassment before I call someone out to look at my a/c problem. You know, trying to avoid the fact that I all I had to do was plug it in... ha/ha. I just moved into an apartment, everything was fine until all of a sudden I...

Air conditioning [ 1 Answers ]

Hi, I have a 4-wire Ritetemp thermostat, my wires are connected right but my unit on the outside will not come on. The blower comes on inside the house, but nothing outside. I not have a pump. And there are no fuses to my unit outside. What do I do?

Air Conditioning [ 3 Answers ]

MY AC won't turn on...


View more questions Search