    GFCI Outlet and Related Circuit Breaker
    I have a 15 amp GFCI outlet that is connected to a 15 amp outside breaker. When using electrical items on the circuit, my outside breaker is tripping without the inside GFCI breakers tripping. I am wondering whether the outside breaker is faulty or should be 20 amps. It doesn't make sense to me that the GFCI breakers are not tripping but the outside one is. Please help.
    tanndog's Avatar
    tanndog Posts: 8, Reputation: 3
    New Member
     
    #2

    Aug 29, 2007, 12:40 AM
    GFCI will only interrupt current if the current going out of the outlet is not equal to that coming in by some set percentage. So if you have a 15 Amp GFCI it will trip when overloaded usually 150% of rating or when something like .5 amps difference from going out to coming back to nuetral. A regular 15 amp breaker will only trip when loaded to usually 150% of its rating. This could be very different based on long time trip setpoint and short time, this is a design of the breaker. I would need more info to help you fully. Does the outside breaker trip when the load first starts or when the load has run for a while? What model breakers are they and what are the trip settings? It sounds like you are experiencing an over load condition for the breaker outside, breakers do go bad but verrrryyy rarely. Is this a new system you have put in? If so were both breakers put in at same time?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Aug 29, 2007, 04:17 AM
    I think you are calling the outside "breaker" a 15 A rated GFCI and the inside "breaker" a 15 A breaker. If this is the case a GFCI means a Ground Fault Circuit Interrupter and will not trip when a circuit is overloaded. The 15 A rating of the GFCI means that you can plug in a item that draws 15 A without damaging the receptacle. They trip for different kinds of faults. "Overloaded" means drawing in excess of 15 Amps. Breakers are not exact. Time and the amount of overload determines whether the breaker will trip.

    20 A services usually require 12AWG wire. 15 A 14 AWG. The breaker should not be changed without changing the wire as well.

    BTW, if two standard breakers are in series they may, or may not trip simultaneously.
    derekwwp's Avatar
    derekwwp Posts: 12, Reputation: 1
    New Member
     
    #4

    Aug 30, 2007, 12:08 AM
    Thanks for both the responses. Tanndog, the breaker outside only trips after the load has been on for awhile. The load that is tripping the outside breaker is a hottub circulation pump and/or inline heater. I also figured out that my garage is on the same GFCI breaker, and I have a full size refrigerator running on that circuit in the garage. It sounds like the loads, when going at the same time, are too much for the circuit and are tripping the outside breaker. Perhaps I could unplug the refrigerator, run the tub, and see if the same thing happens? That may tell me something about the load. This circuit is not a new install. It came with the house that I purchases 12 years ago. But, I recently put in the tub and started experiencing this problem. The breaker specs are as follows:
    Brand looks like SA
    1 pole type MP-T
    MAX.RMS.SYM.AMPS
    10,000 120/240 VAC
    HACR type
    14-10 gauge

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

Gfci outlet [ 5 Answers ]

Hi, I have installed a small pond. I called an electrician to put a GFCI outlet near the pond. He told me I could save a significant amount of money if I dig the trench for the line. Well... I had called Miss Utility before digging the hole for the pond and there is a Cox Cable line that...

Electrical outlet rating vs. Circuit breaker amperage rating [ 5 Answers ]

Hello to all, I am new to this forum, please excuse me if this question has been answered. I just bought a Thermal Dynamics Plasma cutter. It has a Nema 50-P plug end on it, which I assume is to be plugged into a Nema 50-R outlet. In looking in my reference book, this is a 3 wire...

GFCI Circuit Breaker. [ 2 Answers ]

I recently ran a branch circuit to the exterior of the house to add a receptacle on the patio. The existing 15 amp breaker protected a circuit that had only three plug outlets and one switched ceiling light. The circuit is very lightly used. So I want to add GFIC protection in the form of a breaker...

Outside GFI circuit - 15amp outlet on 20amp circuit [ 1 Answers ]

I need a better understanding of what I should do when setting up my new outdoor circuit. I've got a circuit that runs about 150 feet, so I'm installing 10g wire to allow for the voltage drop. I read in the Home Depot Electrical 123 book that I can have at most a 15amp circuit with 10g wire on...


View more questions Search