    Disassembling hubbed cast iron -- lead and oakum
    Hey folks,

    I'm taking apart part of the cast iron main stack in my house (3" hubbed service-weight) to replace a leaky fitting.

    I've used a galvanized saddle clamp, and am pretty happy with the support/blocking/pre-load i have on the main stack, so it's time to take apart the joints and bust that bad fitting out of the basement wall.

    The problem is, the top of the hubbed fitting that i really need to remove is not accessible, hardly at all. I can get a screwdriver on it to just barely scratch the lead, but that's only in one spot on the fitting anyhow.

    My question is..... Can i remove the fittings from below?

    Ie, first break the basement wall and get the combo wye/bend out, then pull off the 3" x 1.5" vent-tee, which is attached to the bottom of the 1/8bend that comes out of the house wall...


    The sequence is like this:

    1/8 Bend (from stack inside house wall)
    |
    1/8 Bend (to make stack vertical again, this is the lowest fitting i need to keep, and has the support clamp on it)
    |
    3" x 1.5" vent-Tee (to be removed and replaced with a Wye, and that PVC routed into it)
    |
    3" x 4" Combo Wye-bend (goes into house foundation, the other end of this inside wall is what's leaking)


    Attached is a quick picture, for those visually inclined.

    What i'm worried about is that without getting the lead out, i won't be able to pull that 3"/1.5" Tee off the rest of the stack. Of course, I'm also wary about standing in the basement and PULLing the stack down towards me!

    Will I be able to wiggle it around and get it free? Do I need to invest in a team of micro-robots to climb in there and dig the packing out?

    Thanks!
    :-)

    ~aaron


    .
    Attached Images
     
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Jul 21, 2007, 01:12 PM
    If the raiser clamp is braced securely then I would simply take a hammer and break out the hub of the tee. I would also cut out the hub underneath and convert to PVC using a No-Hub clamp. Good luck, Tom
    shreefer's Avatar
    shreefer Posts: 2, Reputation: 1
    New Member
     
    #3

    Sep 2, 2007, 10:03 PM
    From your local home center you can rent a soil waste line wrench for about $15 a day.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Sep 3, 2007, 08:14 AM
    Shreefer gave me a bad rating saying, "shreefer disagrees: answered incorrectly" I have over 50 years of working with cast iron and bell and spickit joints. If your going to bad rate me you better put up a reason why and be prepared to to "answer correctly". And like Growler I never heard of a "soil pipe wrench" Please give me a reason for the bad rating and tell us what a soil pipe wrench does. Cheers, Tom
    dkelley's Avatar
    dkelley Posts: 17, Reputation: 1
    New Member
     
    #5

    Feb 27, 2010, 02:16 PM

    http://www.ridgid.com/Tools/Soil-Pipe-Cutters2 They rent them at HD>
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #6

    Feb 27, 2010, 05:34 PM

    You guys arre thinking of a No-Hub Torque Wrench. And what are we doing hassling a 3 year old thread. :? Tom
    scirocco70's Avatar
    scirocco70 Posts: 128, Reputation: 9
    Junior Member
     
    #7

    Feb 27, 2010, 08:23 PM

    Yeah, I fixed this long, long ago.

    For the record (in another thread, I think) the actual, real-best solution was to stick a 24" pipe wrench on that plug, attach about a 4' section of 2" square tubing to it, and do a couple of pull-ups on it.

    I figured that if I was going to crack the fitting anyhow, I might as well crank on the plug.

    It came loose. Possibly soaking the ancient sealant/putty/goop with first PB Blaster (softened it a little) and then Goof-Off (softened it a lot, soak a rag in it and wrap around the area) helped some.

    Anyhow, this horse is loooooong dead.

    ~a
    DIYsometimes's Avatar
    DIYsometimes Posts: 1, Reputation: 1
    New Member
     
    #8

    Apr 4, 2010, 09:16 PM
    I had a situation like this. I took a hammer broke the pipe as flush as I could to the bell end then used a 1/4 inch metal drill bit put as many holes in the lead as I could and then took a screw driver to pry the lead out. This thread may be three years old but the idea for the drill came from another thread. Mapp gas was totally worthless when I tried "softening up" the lead. And mapp burns hotter then propane so if it was going to work it would have.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #9

    Apr 5, 2010, 06:37 AM

    Thanks for the input DIY but why are you piggybacking onto a three year old thread? Tom
    ironjawz61's Avatar
    ironjawz61 Posts: 1, Reputation: 1
    New Member
     
    #10

    Jun 8, 2010, 12:51 PM
    I wish I would've read this stuff before using a map torch to melt the lead. I was wondering why I couldn't wiggle the damn fitting out. I had no clue about this oakum stuff. Anyway, mission accomplished. Thanks guys.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Toilet Install w/ Lead Sleave & Cast Iron Pipe [ 4 Answers ]

I am installing a new toilet. The original construction had a sub floor, which has been removed by the previous owner. Rather than properly seating the flange on the concrete floor, he put tile grout under it to compensate for the wood sub floor that was removed. The old toilet was sitting about...

Oakum and Plastic or Lead with Cast Iron [ 1 Answers ]

Has anyone used plastic filler with Oakum in cast iron joints? I would like to know your opinion on using plastic, and if you like it, what name or brand have you used? Thank you. J

Cast Iron Lead sealed plumbing [ 1 Answers ]

I have an older home that has a vented stand cast iron plumbing (4-6" diameter), and the joints are sealed with lead. I need to rotate one tee joint (runnuig vertically). Do I have to heat the lead to a molten state to allow rotation? I have never worked with lead sealed pipe and while this...

Removing cast iron / lead joints [ 4 Answers ]

Hi; I have a vertical 2 inch cast iron vent pipe that I need to remove to install a medicine cabinet. I have cut it in one spot with a sawzall, but there is also a joint in it where I would like to separate it. The joint appears to be poured with lead. If I heat it with a propane torch to get it...

Lead Pipe/cast iron [ 4 Answers ]

Hi! I just removed drywall to fix a drain from a bathroom sink. I found 1.5" soft lead pipe from the p-trap to a 3" hub on the cast iron stack. Can I use some kind of coupler from the lead pipe to new plastic or do I need to replace the entire length of pipe? If I need to replace, what's a good...


View more questions Search