    Blower motor of Trane XE80 furnace won't start
    I have a Trane XE80 gas furnace. The purge motor and burner go on, but main motor won't run. LED flashing light flashes continuously when burner is on however, when the burner shuts off, the LED light flashes 4 times at an interval. I tried to look for a reset button on the main blower motor but couldn't find one. Can you help me?
    Frdbrkl's Avatar
    Frdbrkl Posts: 94, Reputation: 7
    Junior Member
     
    #2

    Jan 6, 2008, 11:53 AM
    There is no reset for the blower. Try turning the fan on at the thermostat, and cycling the heat. If that works, you have lost a speed leg in the motor, and need a new motor-running it like this will work as a temporary fix-and I stress TEMPORARY. (I currently have a client with the same issue, and this is how he's getting heat until I can get the board in my hands).

    If that doesn't work, troubleshooting blower and related components is in order. Fan relay on control board may have failed, or it could simply be a motor or capacitor problem. Cycle furnace, check for 110v between Common and the Heat terminal of the fan board. If the fan board is providing 110v, the problem is in the motor or capacitor-if not, it's the board. Unless you have a cap checker, the easiest way to check a capacitor is to change it (less than $10). If that fails, you need a motor.
    smandy's Avatar
    smandy Posts: 6, Reputation: 1
    New Member
     
    #3

    Jan 6, 2008, 12:22 PM
    Thanks for your advice. I turned on the thermostat fan and it works. However I had to rotate the motor fan manually to start the main blower motor. Do you think there is a problem with the control board or capacitor?
    Frdbrkl's Avatar
    Frdbrkl Posts: 94, Reputation: 7
    Junior Member
     
    #4

    Jan 7, 2008, 07:01 PM
    It's possible the capacitor is bad-more than likely though, you'll need a motor. The control board is probably fine-it has the fan relay-which seems to be doing its job.

    The capacitor is an easy change, but break out the tools if the motor needs replacing. It's fairly straightforward for the mechanically inclined-but a blower wheel seized on the shaft can be daunting if you don't have the means to take care of it.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #5

    Jan 7, 2008, 09:02 PM
    Capacitors are easy to check if you have an ohm meter. Short it out and remove one terminal. Check with the meter. It should start fairly high and climb off scale. Anything else, and you have a cheap, easy fix.
    therinnaiguy's Avatar
    therinnaiguy Posts: 153, Reputation: 5
    Junior Member
     
    #6

    Jan 8, 2008, 06:16 AM
    Until you get a new blower motor, keep the fan on "Auto". This will run the fan constantly. At least you will have heat.
    Frdbrkl's Avatar
    Frdbrkl Posts: 94, Reputation: 7
    Junior Member
     
    #7

    Jan 9, 2008, 01:48 PM
    He means to turn the Fan switch on your thermostat to "On", not "Auto". I would be leary of running an overheating motor full time though. Use your best judgement-but don't delay the repairs until meltdown, as it will only cost you more to repair at that point.
    smandy's Avatar
    smandy Posts: 6, Reputation: 1
    New Member
     
    #8

    Jan 9, 2008, 02:36 PM
    To All,

    Thanks for the advice. The blower motor went bad and has to be replaced. Help is on the way.

    Thanks Again.
    frank1141's Avatar
    frank1141 Posts: 1, Reputation: 1
    New Member
     
    #9

    Nov 23, 2012, 10:00 AM
    What size generator in amp range would I need to run the furnace of my Trane xe 80?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace blower motor start and keeps running won't stop [ 12 Answers ]

I have a Carrier central furnace (furnace model 58GP050-BA). Now with the thermostat off the fan set to auto and the Gas pilot is on. When turn on the power switch to the furnace, the blower motor start and keeps running and won't stop. I have to turn off the power switch to the furnace to turn the...

Furnace Blower motor [ 10 Answers ]

Should the furnace blower motor fan be set to auto or on? Which is best for the home? For the motor?

How to remove a Trane (XL80) furnace Blower? [ 1 Answers ]

My Trane (XL80) furnace had been making rattling noise when it kicks on (both AC and Heat). I notice the rattling noise came from the blower. Sounds like the blower's not stable, perhaps, the balance weight or something came off. Is there anyway I can take out the blower and check it out? Is it...

Furnace blower motor [ 1 Answers ]

A friend asked help about his furnace blower emitting a screeching sound during operation and then just stopped. I went over and tried to rotate the blower by hand - resistance to free rotation was present. Removed the blower assembly and dismantled motor. No lubrication on both motor bushings....

Squeaky Trane Blower Motor [ 1 Answers ]

Noticed last night that my Trane furnace was squeaking like a cricket when the air conditioner was running. Then every so often it would make an awful squealing sound like maybe a motor was getting stuck and unable to turn. From reading other posts I'm guessing that I might have a bearing or belt...


View more questions Search