    Outlet tester reads OK but GFCI still trips
    When I rewired my house 5 years ago I installed a GFCI outlet in the main bathroom. On the same line, after the GFCI, is another outlet in that bathroom, a junction box in the attic, an outlet in my small bathroom and then the wall switch to control the lights and fan in the small bathroom.

    Through the years I would run into a problem every now and then. It seemed if I turned on the light and fan in the small bathroom at the same time or in quick succession, the GFCI would trip. I always assumed it was a faulty wall switch until last month when the GFCI will not reset.

    I tried replacing the GFCI, twice, but that didn't solve the problem. In trying to work my way back through the line I snaked through new lines from the junction box into the small bathroom today... still no luck. The breaker in the panel doesn't trip, just the GFCI. When I bypass the GFCI everything works fine and the breaker still doesn't trip. I'm guessing there has to be a small amount of electrical leakage/drain somewhere in the line but when I plug in an outlet tester it reads that everything should be fine.

    Before I start opening up the walls in my main bathroom, does anyone have any advice?

    Thanks,
    Logan
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Feb 23, 2013, 02:13 PM
    You have lights, outlets and a fan on this circuit all downstream of the GFCI...
    Try removing individual items from the circuit and reset the GFCI, see which one is the culprit...
    My nickel is on the fan!.

    If this doesn't reap positive result, I would consider taking all the downstream devices off the load side of the GFCI... none of them are required to be protected except for the receptacle in the small bathroom which you will need to change to a GFCI...

    The amount of ground fault current to trip a GFCI is .005 amperes (5 mA) a very small amount. Sometime long conductor lengths that are GFCI protected will cause tripping also...

    Good Luck
    logan176's Avatar
    logan176 Posts: 341, Reputation: 6
    Full Member
     
    #3

    Feb 23, 2013, 06:15 PM
    It's not the fan but I like what you said about pulling the other items off the line if I rewire. I started at the end of the line and started pulling things off as I worked my way upstream. I pulled everything off and it still tripped. Eventually I disconnected the incoming wire from the junction box that's in between the two bathrooms and wire nutted the end of it to an extension cord with a female end... still no luck. So all I had left was the GFCI, the wire leading out, and the extension cord attached to the end. I tested the line and it seemed fine until I plugged in a lamp.

    Now all I have downstream of the GFCI is a wire. This is what is making me believe that I have to open the wall in the bathroom. Yes?
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #4

    Feb 25, 2013, 05:25 AM
    Tell me, if you disconnect the "load" conductors off the GFCI, does it trip?

    As I tried to suggest, remove everything from the "load" side conductors of the GFCI... then
    Install a new GFCI at the second bathroom. Avoid putting anything on the load side of that GFCI also...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

GFCI trips? [ 11 Answers ]

I have aan outdoor outlet on the patio. On the inside of the wall of the basement (about 6-7 feet away)there is a GFCI outlet. When I plug my Greenlee GT-10 GFI tester into the outlet on the patio it trps the GFCI outlet inside the basement. Slso, when I plug the tester into the inside...

No power to 7 outlets, breaker stays on, & tester reads open neutral [ 5 Answers ]

This is an 1968 house with AL wiring. All of the outlets are new and AL compatible with anti-oxidizer paste. Starting with the first box, I pig tailed each neutral (white) wire together to see if I had a bad outlet. I went from box to box and when I came to the last box, the tester still read open...

Gfci trips [ 3 Answers ]

I have a small fountain motor (not submersible) plugged into a gfci and After working fine for a year it now trips after about 10 minutes. This is What I have tried so far. 1. I plugged a lamp into the same gfci and it stayed on for over 3 hours Until I turned it off - didn't trip. 2....

Outdoor electrical outlet keeps tripping gfci outlet [ 3 Answers ]

Until just recently my christmas decorations would light up when we plugged them into the outdoor electrical outlet. Now when we plug it in the gfci outlet in the garage keeps getting tripped and the lights won't come on. Even when we reset the gfci, once we plug in the chord it gets tripped...

Voltage tester gives false positive reads when line is not hot [ 3 Answers ]

Pro did my rough in. I'm installing outlets, switches, etc Using $20 no contact voltage tester - with plastic tip that beeps/lights when line is hot. I get beep/light even if line is absolutely, definitely dead? For example: 12/3 wire direct from panel to switch box Nothing between panel...


View more questions Search