    GFI outlet vs GF breaker
    Is there a difference functionally between a GFI outlet and a GFI breaker? I am installing a jetted tub in the basement. The water pump has the two loose wires (+ground) and indicates the connection to be made in junction box and be protected by a GFI. A GFI for my type breaker is $300. I had an electricion advise I could just attach a plug at the breaker box end of the wire run and then plug this into a GFI receptical which would be connecteced to a non GFI breaker. Can this be done?

    The in line heater simple came with a plug already attached so I was just going to plug directly into a GFI receptacle. Why the difference in connection. One with plug attached the other with loose wires?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 9, 2006, 04:35 AM
    What is the voltage required by the pump and heater? I suspect that one is 120 volt, and the other is 240 volt.

    The 120 volt unit with the cord can plug into a GFI outlet.

    The 240 volt unit cannot plug into a GFI 240 volt outlet, and must be connected to a circuit breaker.

    You say the pump has wires, and the heater has a plug. Usually the heater draws much more current, and is usually 240 volts, and the pump is usually 120 volt. Sounds reversed.

    Please check to be sure which is which.

    Check the amp rating of the 240 volt circuit, and be sure to know which brand of panelboard you have, may be GE, Square D, Seimens, Murray, etc.

    Also, be sure to ask for the correct 2 pole 240 volt GFI breaker, if you do not need a neutral for the tub, then get a CB with out a neutral connection.

    Find an electrical supplier that handles that brand and ask for pricing to compare the price you already have, probably from Home Depot or Lowe's.

    There are many websites that electrical material and breakers can be purchased, give them a try.
    cdnk5's Avatar
    cdnk5 Posts: 14, Reputation: 2
    New Member
     
    #3

    May 9, 2006, 05:45 PM
    Thanks for the quick response.

    In-line heater is 1500W 120V 12A while the pump is 115V 7.5A. It's a very small heater (about the size of a can of Red Bull). These were the ratings right on the units themselves.

    Panel is a Commander using QBH type breakers. Tried all local big box who don't stock. Online price was in the hundreds. Local electrician the same. That's why I was hoping to be able to use the $15 GFI receptical instead if possible.

    Ty
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    May 9, 2006, 06:08 PM
    I see no reason to splice, in a box, the heater leads onto a piece of #12-3 SJ or SJO cord, no longer than six feet, and plug into a good quality GFI outlet. Try to keep this outlet under the tub if possible, in the utility area, and be sure it is kept dry, along with the pump outlet.

    It came with no cord as it is how it comes from the manufacturer of the heater.

    Cannot say I ever heard of the panel, some brands are regional. But sounds like your all set using the GFI outlets.

    And even thou a 15 amp circuit will work fine, I suggest a 20 amp circuit with 20 AMP GFI devices and all #12 wire.

    Check the manufactures instructions for grounding instructions. Probably mostly no metal, and just need to ground the heater and the pump frame.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can you use a 15 amp outlet on a 20 AMP breaker with 12-2? [ 13 Answers ]

I have a few questions that I need help on. I recently moved into my home and discovered a few things. 1. 12-2 wire has been ran throughout the house. Can you use a 15 amp outlet on a 20 AMP breaker with 12-2?? 2. How many lights would you say you can run on 12-2 and/or 14-2 wire? 3. How...

Gfi outlet [ 6 Answers ]

I just moved into the house in May. I believe the gfi outlet was working when the inspector inspected our house, but it seemed soon after it stopped working. We tried to press the reset button just in case the test button was pressed and nothing happens (meaning it won't depress or anything). Just...

Grounding an Outlet [ 22 Answers ]

I am moving into an older house that has only 2-prong outlets. Some are 3-prong, but they are not grounded (I have a power strip that tells you if it is gounded or not). I found this at Ace Hardware....

120 volt outlet from 240 volt outlet [ 1 Answers ]

I understand that it is possbile to wire a 120 volt outlet from a 240 volt outlet. My 240 volt outlet has 3 wires in, white, black, and a ground. Do I wire the 120 volt outlet from the either wire and the ground? My voltage meter indicates that connection is 120 volts. Is there any down side to...

Outside outlet problem [ 2 Answers ]

Hello anyone, This is the first time I've done this so I hope I explain this O K I have an outlet on the outside of my home ,actually there are two, One in the front and one in the back of the house. Whenever I plug anything like Christmas lights or the swimming pool filter into either of...


View more questions Search