  1. Question: Base board heat

    by tkrussell
    Answers
    1
    Views
    806

    What kind of help do you need? If you want to...

    What kind of help do you need? If you want to troubleshoot this problem what knowledge and tools do you have to work on electrical wiring? If there is a transformer, then you must have low voltage...
  2. It is a low voltage transformer, with anywhere...

    It is a low voltage transformer, with anywhere from 6 to 24 volt output, probably provides voltage for your doorbell.
  3. Answers
    5
    Views
    1,067

    An open ground test at a receptacle means that...

    An open ground test at a receptacle means that circuit has an open ground between the receptacle and the panel. You may not have a ground rod, althou there should be at least one, your system may be...
  4. Answers
    5
    Views
    1,067

    Need to know more details as to why you believe...

    Need to know more details as to why you believe this needs to be done. Grounding of a service is simple and should had been done by the installer. Just arbitrarily connecting a grounding electrode...
  5. Answers
    5
    Views
    4,692

    Usually a blue test button on the front of each...

    Usually a blue test button on the front of each breaker, depending on the brand. During a power failure, oft times it is not a clean break, so to speak, could be something weird happened at the place...
  6. Answers
    5
    Views
    4,692

    Any chance the tripped breakers are Arc Fault...

    Any chance the tripped breakers are Arc Fault type? Some times a power failure can cause voltage surges that cause breakers to trip. There are devices on the grid call Reclosers, for example, if a...
  7. My guess is you have a three way switch setup,...

    My guess is you have a three way switch setup, two switches that control one light. If your not familiar with this wiring arrangement and do not know how to troubleshoot the system, you will need to...
  8. I suspect the washer/dryer wire is #10 aluminum,...

    I suspect the washer/dryer wire is #10 aluminum, which is the correct size for a 20 amp circuit using AL wire. Inform your friend, if there is ever a property insurance inspection of the building,...
  9. No additional GFI devices are needed as long as...

    No additional GFI devices are needed as long as the new receptacles are GFI protected by the interior device.
  10. Some photos of the fixture would be helpful.

    Some photos of the fixture would be helpful.
  11. Answers
    2
    Views
    5,103

    Are all the lights working? What happens if one...

    Are all the lights working? What happens if one breaker is turned off, then the other is turned off? Exactly which slots are the breaker located in the panel?
  12. Answers
    2
    Views
    5,379

    So the electrician that installed it violated two...

    So the electrician that installed it violated two codes, did not attach to the structure, and left it with no cover? If you see surface rust, then there is corrosion inside the receptacle, and needs...
  13. Answers
    3
    Views
    5,390

    That fact does not matter. All grounding must be...

    That fact does not matter. All grounding must be done at the first Main Disconnect.
  14. Answers
    3
    Views
    5,390

    No, since the Main Breaker is at the pole, the...

    No, since the Main Breaker is at the pole, the feeder must be 4 wire to the home, for the two hots, one neutral and one equipment ground, with the ground rod driven at the pole grounding both the...
  15. Answers
    2
    Views
    5,191

    There are literally hundreds of styles of...

    There are literally hundreds of styles of micro-switches available. If you were to look thru:...
  16. Which one of the four choices was discussed in...

    Which one of the four choices was discussed in the class?
  17. Question: Doorbell

    by tkrussell
    Answers
    1
    Views
    5,459

    Either the new button is defective, or you got...

    Either the new button is defective, or you got the wrong button which is now a closed switch until pressed.
  18. Answers
    1
    Views
    5,693

    http://www.upm-marketing.com/manuals/RC420_TR310.p...

    http://www.upm-marketing.com/manuals/RC420_TR310.pdf
  19. Answers
    2
    Views
    5,459

    Do you have a question?

    Do you have a question?
  20. Answers
    5
    Views
    849

    In the event you do not hire a professional, you...

    In the event you do not hire a professional, you must be informed that any open flame appliance located in a garage must be installed at least 18 inches above the floor, as in the vent of a fuel...
  21. The A15 and the A19 number is the designation of...

    The A15 and the A19 number is the designation of the bulb size, not the medium base. Bases or socket numbers begin with "E". The diameter of lamps is measured in 1/18ths of an inch, so the A15 lamp...
  22. Answers
    13
    Views
    1,931

    This is not true, first see Section 404.9(B)...

    This is not true, first see Section 404.9(B) above.

    Second, there are two types of switches available, if self grounding, then no equipment ground is needed:

    1221-2 > Toggle > AC Switches >...
  23. Answers
    13
    Views
    1,931

    Stan, can you review 404.9 (B)? Section 404.9...

    Stan, can you review 404.9 (B)?

    Section 404.9 (B) Grounding. Snap switches, including dimmer and similar control switches, shall be connected to an equipment grounding conductor

    The above...
  24. Answers
    13
    Views
    1,931

    They only hold the screws onto the device....

    They only hold the screws onto the device. Removing them have no affect on grounding.
  25. Answers
    1
    Views
    955

    You would be best contacting Nutone directly to...

    You would be best contacting Nutone directly to learn what they have as a replacement.

    NuTone Customer Service
  26. Question: Electrical

    by tkrussell
    Answers
    1
    Views
    500

    Each phase can handle 200 amps.

    Each phase can handle 200 amps.
  27. Answers
    1
    Views
    511

    36 inches assuming it is opposite an insulated...

    36 inches assuming it is opposite an insulated surface.

    42 inches if opposite a grounded surface, (ie: concrete wall)

    48 inches if opposite other switchgear.
  28. Question: 480v 3p panel

    by tkrussell
    Answers
    9
    Views
    725

    Don, the title of the post is 480v 3p panel , I...

    Don, the title of the post is 480v 3p panel , I do not think this is residential.
  29. Will not hurt to give it a try.

    Will not hurt to give it a try.
  30. Question: 480v 3p panel

    by tkrussell
    Answers
    9
    Views
    725

    If a fluid line needs to be above a panel in the...

    If a fluid line needs to be above a panel in the dedicated space above the panel, a drip pan is allowed to be installed below the piping and above the panel to protect the panel.
  31. Answers
    6
    Views
    862

    Often, the action of turning on a switch can...

    Often, the action of turning on a switch can cause a AFCI breaker to trip, a worn out switch will cause excessive arcing in the switch.

    Replace switch.
  32. Answers
    2
    Views
    615

    In addition to needing more details, you need to...

    In addition to needing more details, you need to re-word your question.

    The way I read:

    what size of wire guage do I need to fuse a 200A gear switch

    Sounds like you want to use a wire as a...
  33. Answers
    11
    Views
    1,252

    A feeder conduit can contain wiring from other...

    A feeder conduit can contain wiring from other branch circuits, conduit just needs to be large enough. The 2" PVC Sch 40 conduit you propose is large enough for the 3 - #1 AL XHHW, 1 - #6 Al XHHW...
  34. Answers
    15
    Views
    1,917

    Explain to POCO that if the problem is with any...

    Explain to POCO that if the problem is with any of their connections, at the transformer or at your service connection, they are liable for any damage done in your home.

    For most POCO, any...
  35. Answers
    13
    Views
    1,931

    If the switches have a green ground screw, yes,...

    If the switches have a green ground screw, yes, connect each to ground, and connect to the metal box.Do not remove the insulators.

    This is all per the National Electric Code, which each state...
  36. Here is the NYC electric code, which amends the...

    Here is the NYC electric code, which amends the 2008 edition of the NEC:

    http://www.nyc.gov/html/dob/downloads/bldgs_code/electrical_code_local_law_39of2011.pdf


    And seems they do not have any...
  37. Answers
    15
    Views
    1,917

    A qualified electrician that has access to power...

    A qualified electrician that has access to power recording instruments needs to come in and record your power to confirm the voltage is fluctuating, causing the lights to flicker.

    By using a...
  38. Question: Electrical help

    by tkrussell
    Answers
    3
    Views
    637

    DO NOT Use a 40 amp Breaker on 20 amp wiring! ...

    DO NOT Use a 40 amp Breaker on 20 amp wiring!

    There is no such thing as a 140 amp panel or service.

    You are not allowed to do your own electrical work in any building that is not your own...
  39. Answers
    16
    Views
    45,673

    And the problem was solved:

    And the problem was solved:
  40. Most, if not all, homes have 120/240 volts in the...

    Most, if not all, homes have 120/240 volts in the service.

    What you need is to hire an electrician to check the amp size of the service, and confirm the service has sufficient amp capacity to...
  41. I moved this to the correct forum. The...

    I moved this to the correct forum.

    The difference between a 100 amp service and a 150 amp service is 50 amps additional capacity on the 150 amp service. I am sure you knew that already, and I...
  42. Answers
    20
    Views
    1,147

    Any "friend" that wants you to "show" something...

    Any "friend" that wants you to "show" something on cam is not a friend. Just someone that wants to get off on seeing whatever you have to show, and wants to degrade and cheapen you.

    Next time your...
  43. Answers
    6
    Views
    1,110

    What was the outcome of the power companies...

    What was the outcome of the power companies visit? This does need to be corrected ASAP, as the dimming can damage motors such as refrigerators, and the brightening can damage anything by the...
  44. Question: Wiring size

    by tkrussell
    Answers
    14
    Views
    1,171

    Whip on an appliance that is installed by the...

    Whip on an appliance that is installed by the manufacturer is different than a whip that must be installed in the field. The whip on the appliance was present, tested and listed by UL as is.

    The...
  45. Answers
    3
    Views
    349

    Two separate but related questions merged. Enter...

    Two separate but related questions merged. Enter all information in one question.
  46. Either there is a short circuit in the wiring or...

    Either there is a short circuit in the wiring or heating elements, could be a chance the breaker is defective.

    I merged your two questions. Just enter all information in one question.
  47. Answers
    1
    Views
    778

    Task List: #1. Hire electrician- Check The...

    Task List:

    #1. Hire electrician- Check

    The electrician will determine what needs to be done, once he learns what each new device needs for power, and will determine if the 50 amp feeder is...
  48. Question: Connecting load

    by tkrussell
    Answers
    4
    Views
    901

    If you knew that why did you ask? And now you ask...

    If you knew that why did you ask? And now you ask about a 10 kW motor, as if we were suppose to know what you meant?

    A 10kW motor will not draw the same lower current of a 2 kw motor.

    How do...
  49. Since it is obsolete, it cannot be found on the...

    Since it is obsolete, it cannot be found on the internet, so we do not know the generic details. Can you describe it, where is it installed, perhaps provide a photo?
  50. Question: Connecting load

    by tkrussell
    Answers
    4
    Views
    901

    Stan makes a good point, but assuming both motors...

    Stan makes a good point, but assuming both motors are drawing nameplate watts, the difference is 1.1kW, and one hour is 1.1 kiloWatt-hour.

    Even if the 2.2kW motor was not running at full load, the...