  • Aug 28, 2009, 06:43 PM
    cheaphouses
    Ground bar and neutral bar
    I was working on a rehab project, and the guy working on the wiring was installing both the ground wire and the neutral wire together into the ground bar or neutral bar, depending on the side of the circuit.

    I was always under the impression that ground wires to ground bar and neutral wires to neutral bar.

    Is the above technique safe?

    When I asked him about it, he said it makes the wiring in the box neater.
  • Aug 28, 2009, 07:01 PM
    stanfortyman
    Quote:

    Originally Posted by cheaphouses View Post
    I was always under the impression that ground wires to ground bar and neutral wires to neutral bar.

    In the main panels there is no difference between the ground bar and the neutral bar.
    I will say, an add-on ground bar that is screwed to the back of the panel must ONLY be used for grounds.



    Quote:

    Originally Posted by cheaphouses View Post
    Is the above technique safe?

    Code complaint? Definitely not.
    Safe? I think so. Some will disagree.
    The part that is non-complaint is that a neutral wire must be one wire to a termination.
    Grounds (of the same size) can usually be doubled or even trippled up in a single hole.



    Quote:

    Originally Posted by cheaphouses View Post
    When I asked him about it, he said it makes the wiring in the box neater.

    I do agree with this.


    This is a practice I followed for many years. I only stopped doing this about 7-8 years ago by choice. The inspectors in my area had no problem with it.
  • Aug 28, 2009, 07:13 PM
    KISS

    Hard to say, but let's clarify:

    If there is an isolated neutral, then ground and neutral must be separate. There is a green screw that is usually removed to isolate the neutral. In these cases, usually a ground bar kit needs to be purchased to get the ground bar back. This occurs on sub-panels although not exclusively.

    If there isn't an isolated neutral, then it makes no difference.

    The neutral to ground bond usually occurs at the first disconnect, so for houses with an outside disconnect, the inside panel will have an isolated neutral.

    In many cases the first disconnect is at the main panel and therefore the neutral and ground connections are essentially the same.

    Purists would prefer a separate ground and neutral in both cases bonded at one point for other reasons such as electrical noise and power quality issues.
  • Aug 29, 2009, 04:13 PM
    TGMcCallie

    Why did the inspector want my electrician to separate the neutrals and grounds when I had electrical work done. This is in my main breaker box.

    Was that just because he preferred it like that?
  • Aug 29, 2009, 04:16 PM
    stanfortyman
    Quote:

    Originally Posted by TGMcCallie View Post
    Why did the inspector want my electrician to seperate the neutrals and grounds when I had electrical work done. This is in my main breaker box.

    Was that just because he preferred it like that?

    Who knows. Was there a main disconnect outside?
  • Aug 29, 2009, 04:56 PM
    TGMcCallie

    I had my meter center moved to another location due to remodeling. The electrician installed a meter center that had a breaker box incorporated in it sort of like they use in mobile homes. He did this so he could run a 100 amp service to my shop and have some extra breakers there at the meter center. As far as a main disconnect outside, the only one I know about is the main breaker in the main breaker box in my garage.
  • Aug 29, 2009, 06:03 PM
    stanfortyman
    Quote:

    Originally Posted by TGMcCallie View Post
    As far as a main disconnect outside, the only one I know about is the main breaker in the main breaker box in my garage.

    But you just got finished describing about the new "meter center" that he installed with breakers outside.
    So is there or isn't there a main breaker outside?
  • Aug 29, 2009, 08:28 PM
    TGMcCallie

    There is not a main breaker outside that cuts off the power coming into the house. There is only one Main Breaker and that is in the main panel box inside the garage.
  • Aug 29, 2009, 08:33 PM
    KISS

    Is the neutral/ground bond in the meter base?
  • Aug 30, 2009, 08:44 AM
    TGMcCallie

    Meter base? Are you talking about where the actual meter is or the main breaker box? I don't know how it is in the meter center but in the main meter box they are bonded.
  • Aug 30, 2009, 11:05 AM
    KISS

    They can make the body nearly anywhere. Usually it's the first disconnect. This is the bet place to put it. You need to figure out where neutral and ground come together for the first time.
  • Aug 30, 2009, 02:11 PM
    TGMcCallie
    If the entrance cables are grounded at the transformer why is there a separate grounding rod at the main breaker box or meter center?
  • Aug 30, 2009, 02:33 PM
    donf

    TG,

    I just answered the question you posted.

    First, only the Neutral is grounded at the transformer. Neutral is also referred to as the "Grounded Conductor" and it provides the return path from the residence back to the transformer.

    The two hot cables are referred to as "Ungrounded conductors"

    At the main panel (only) Neutral and ground are tied together. Also the ground rod and EGC (Equipment Ground Conductor) are tied to the main panel.

    The grounding system at the main panel does several things, one of which is to tie the service's Neutral to the earth ground at the panel. This prevents a ground loop.

    Also, the residence's ground protects people from electrocution and carries electrical faults and stray charges away to earth ground.
  • Aug 30, 2009, 02:40 PM
    TGMcCallie

    I am sorry but I thought I had edited and removed this from this post and posted it in a separate one.

    Thanks
    Tom
  • Oct 13, 2013, 07:42 AM
    BigC1942
    I am adding a 100 amp Square D load center to my workshop. I have attached the 2 hot wires and the neutral wire to the panel and the but I do not see a place to attach the ground wire. Where do I attach the Groud wire?
  • Oct 13, 2013, 07:48 AM
    BigC1942
    I am adding a 100 amp Square D load center to my workshop. I have attached the 2 hot wires and the neutral wire to the panel and the but I do not see a place to attach the ground wire. Where do I attach the ground wire?
  • Oct 13, 2013, 07:52 AM
    hkstroud
    1 Attachment(s)
    You add a grounding buss to the panel.
  • Oct 13, 2013, 10:26 AM
    KISS
    Not exactly. Get a sub-panel conversion kit which should be made for your panel.

    It will contain ground bars like above,

    The instruction for the panel should show how to isolate the neutral/ground bus in a main breaker panel. Usually you remove a screw and add the ground bar(s).