  • Dec 25, 2007, 10:18 AM
    bronarlie
    Gas valve will not open on intertherm furnace blower is stuck
    Intertherm furnace pilot is lit but burner will not I have 24 volts at valve
  • Dec 25, 2007, 10:23 AM
    hixton
    Has the furnace ran this year or is this the first time ?
  • Dec 25, 2007, 10:35 AM
    hvac1000
    Make sure the rocker switch if so equipted is on heat.
    Make sure thermostat is on heat and turned up.
    On many mobile home furnaces there is a small button in the center of the high limit control which on most furnaces is located on the left side of the blower near the back on most units if it is downflow style. Push the button to reset.
  • Dec 25, 2007, 11:33 AM
    bronarlie
    Quote:

    Originally Posted by bronarlie
    Intertherm furnace pilot is lit but burner will not i have 24 volts at valve

    Sorry about the inapppropiate post first time user will try to do better. Fur is about 74 model intertherm high limit has no reset furn has been used this year worked fine till yester day
  • Dec 25, 2007, 05:03 PM
    hvac1000
    Start by tracing the 24 volt circuit from the beginning at the transformer through the components of the furnace. When the voltage stops you have found your defective part.