  • Apr 27, 2007, 06:20 PM
    kdeweeh
    My Steam Shower keeps throwing the breaker!
    Hi Everyone, I have just installed a steam shower bath and it takes 3KW and I have it on a 20 Amp breaker. I thought that would be enough amps to carry it; what could be wrong? Thanks. Kaye
  • Apr 27, 2007, 06:27 PM
    caibuadday
    Quote:

    Originally Posted by kdeweeh
    Hi Everyone, I have just installed a steam shower bath and it takes 3KW and I have it on a 20 Amp breaker. I thought that would be enough amps to carry it; what could be wrong? Thanks. Kaye

    20 amp with 120v at max is less than 2400w. What the volt?
  • Apr 27, 2007, 06:51 PM
    Kerrveball12
    I assume you are running this from 120V, because at 120V it will pull 25A. At 240V it will only pull 12.5A. So up the breaker, and you should be OK.
  • Apr 27, 2007, 07:09 PM
    kdeweeh
    Quote:

    Originally Posted by caibuadday
    20 amp with 120v at max is less than 2400w. what the volt?

    Hi, It is 120V. I guess I need to up the breaker?
  • Apr 27, 2007, 08:28 PM
    caibuadday
    Quote:

    Originally Posted by kdeweeh
    Hi, It is 120V. I guess I need to up the breaker??

    Up the breaker to 30A and wire to #10
  • Apr 28, 2007, 07:20 PM
    shuntripper
    Don't put that 30a CB on less than 10 gauge wire, 2400W/120V = 20A draw but you're not supposed to be over 80% of the CB rating. Actually code says CB not less than 125% of load (for this)