View Full Version : 220 wiring with only 3 wires
goldmoma
Jun 1, 2007, 05:17 AM
I am trying to wire my window air conditioner to my breaker panel. I only have 3 wires. One black, one white and the ground. How do I connect the wires to the 220 breaker in the panel. My outlet only has 3 wire connection so I know how to connect that. Just not sure how to connect in the main panel with only the 3 wires.:confused:
tkrussell
Jun 1, 2007, 05:21 AM
Connect the black and white to the load side terminals of the breaker, one wire to each terminal. Re-mark the white wire with black tape at both exposed ends in the panel and the outlet box to indicate that the wire is now being used as a live wire, and not a neutral.
Connect the bare or green ground to the equipment ground bar in the panel.
I can only assume the circuit breaker and wiring is sized properly for the air conditioner.
goldmoma
Jun 1, 2007, 11:26 AM
The a/c is 14,000 BTU. The wire I am using is 12/2 indoor romex.
wallepoid
Jun 10, 2007, 07:14 AM
How to wire - 3 wire 220V connection to circuit breaker for window air conditioner.
tkrussell
Jun 10, 2007, 07:53 AM
Did you read the answer I provided?
Stratmando
Jun 10, 2007, 08:19 AM
This wire needs to be for Air Conditioner ONLY. If other recpticles on same wires. You could
Destroy TV, Lights, anything that shouldn't see 220.
goldmoma
Jun 11, 2007, 05:40 AM
Thanks for your help. I was able to wire my a/c properly with your advise and it works beautifully. Thanks again.