Aug 14, 2020, 05:16 PM
hi i would like know if a ground wire can be ran from the neutral bus bar inside the main panel to a ground electrode.
tkrussell
Aug 15, 2020, 08:09 AM
Need to know more details as to why you believe this needs to be done. Grounding of a service is simple and should had been done by the installer. Just arbitrarily connecting a grounding electrode conductor to the neutral is not allowed. Please describe the situation you have. Where is the meter? Is there a main circuit breaker at the meter or located in the main panel?
Also, just noted this question is posted in Cars & Trucks, perhaps admin can make the necessary corrections. >Admin moved<
minibike6969
Aug 19, 2020, 09:16 PM
i pluged in a circut tester and the light came on saying there is a open ground,and i see nothing as far as a ground wire going to earth copper rod,also if i were to add a ground wire to the electrical panel box then to a grounding rod would that fix the open ground problem
tkrussell
Aug 20, 2020, 04:25 AM
An open ground test at a receptacle means that circuit has an open ground between the receptacle and the panel. You may not have a ground rod, althou there should be at least one, your system may be grounded to the utility water line.
minibike6969
Aug 21, 2020, 07:17 AM
no ground to water line, but the two wire electrical system jacket is metal
talaniman
Aug 22, 2020, 07:29 AM
https://www.hunker.com/13401948/how-to-tell-if-your-house-wiring-is-grounded
https://getscribeware.com/understanding-open-grounds-and-options-for-repair/
Or does this sound like your condition
https://www.hunker.com/12436135/what-is-an-open-neutral
Hard to diagnose or advise with limited data, so I can only put forth processes and hope you use them SAFELY.