PDA

View Full Version : Can you run a 20 amp gfci off a 30 amp breaker?


bbobball
Oct 7, 2018, 04:04 PM
I want to run 100 feet of 10/2 wire from a 200 amp box using a 30 amp single pole breaker then into a junction box to connect to 12/2 wire then to a 20 amp GFCI to lights and outlets. Is this correct use of materials to go that far?

donf
Oct 8, 2018, 10:41 AM
NO!

You have 2 choices. Use your 10/2 for your run from the panel board, but use a 20 amp breaker. Or use a 20 amp Breaker and 12/2 for the entire circuit

You must protect the smallest wire at it's listed amps, in this case 20 amps.

Not knowing exactly what you are planning to do, I'm a little concerned.

For example using a standard voltage drop calculator a run of 150' (end to end) the calculator says you need to use a #8 AWG feeder to keep the voltage drop to 3.5%.

The NEC "Recommends" not mandates that there be no more than 5% VD end to end.