View Full Version : Will a 20 amp thermostat work on a 21 amp circuit


BTU BOY
Feb 6, 2017, 03:47 PM
I want to add a remote thermostat that is rated for 20 Amps. I used a clamp amp meter and read 21.5 amps will it be OK? What is the safety factor of a thermostat?

ballengerb1
Feb 6, 2017, 05:54 PM
Thermostats most frequently run on 24 volts so could you explain your situation further? What brand and model are you trying to use?

ma0641
Feb 6, 2017, 06:14 PM
Electric baseboard heat?

Missouri Bound
Feb 6, 2017, 09:29 PM
To answer your question as posted... no.

Stratmando
Feb 20, 2017, 12:58 PM
If power goes through Thermostat. You may want to add a contactor to carry the Load, Then you could use other thermostats and load would not need to run to thermostat. Just control wires, Could use the current conductors(#10 or larger for control)
Over 20 amps, you would need at least #10 wiring.