View Full Version : Lennox g40uh error. Furnace won't heat


needHVAChelp
Feb 9, 2016, 08:10 PM
Lennox g40uh error "Primary or Secondary limit switch open"

I have test the continuity on both limit switches and on the flame roll over switches. Along with a few other things. Could it be the control board?

ma0641
Feb 9, 2016, 09:31 PM
Found this in the manual under troubleshooting. The ignition control is equipped with two LED lights for troubleshooting. The diagnostic for that code is: LED #1 slow flash, LED#2 is on
"Primary or secondary limit switch open. Limit must close within 3 minutes or unit goes into 1 hour WatchGuard." That is what you are getting? Did you check the high limit?
Are you locked out in the Watchguard?