Hey everyone I get this problem
Every year around fall here in Calgary, AB. I built my house new in 2010 and every year the furnace fails to start because water is built up I. These clear plastic tubes that causes the error "pressure switch open with inducer on". Now I've checked the venting and it appears to be OK and the builder installed this but really getting annoying now to the point that every year I have to drain water.
My question is what should I be looking for to see if perhaps the drain is clogged or may be its not vented properly? Or anything that anyone can think of? I'll try to get some pictures Nd upload it.
bitters
Oct 29, 2014, 03:07 PM
Yes pics would be good. What is the name and model number? It sounds like the trap is working. This is a common problem on condensing furnaces.
Dayclone
Oct 29, 2014, 08:32 PM
So I've I took all the tubes off and made sure nothing is plugged and the exhaust and intake pipes are good. Drained the water but unit still doesn't start.
I get an error code 3 flashed that says pressure switch open and inducer on
I tried jumping the pressure switch leads to get it on but I'm sure I am doing it wrong cause it won't Fire up. There was a few times that I was able to get it to fire up but lasted 3 seconds.
It's a aire flo CG92TB
http://i58.tinypic.com/a3mlb7.jpg
http://i57.tinypic.com/ru4m5i.jpg
http://i58.tinypic.com/6o2xli.jpg
Grady White
Oct 30, 2014, 07:36 AM
Sometimes over the summer pressure switches will get stuck. Reset the furnace & once the inducer starts, rap on both pressure switches with a screwdriver handle or something similar. This may or may not help but it sometimes does.
Dayclone
Oct 30, 2014, 11:39 AM
I had my gas company out and he said the slope wasn't done correctly to drain. As well as there could be a weak pressure sensor switch but they usually rarely fail. I'm thinking that water backed up to the inducer and possibly caused it to rust and caused the pressure switched to trip, but I am not sure, it was brand new 4 years ago and I've had this issue every year since.
Installed by Arpi's and Homebuilder is Brookfield Homes.
Grady White
Oct 30, 2014, 11:46 AM
The slope on the exhaust should be at least 1/4" per foot of run. It needs to slope upward from the furnace to the outdoors. Any sags or droops in the exhaust line will cause problems.
Dayclone
Oct 30, 2014, 05:29 PM
Grady,
It's definitely 1' long but doesn't appear to even slope... It's straight horizontal. I'm going to see if I can get it to slope, have to cut the pipe shorter the one that runs vertical to the furnace. You see these guys are pro's too, you pay them to install it and you'd think they know what they should be doing.
Steve
Grady White
Oct 31, 2014, 11:25 AM
Can you post a couple of pictures of the exhaust run? Here is a link to the installation manual http://www.aireflo-hvac.com/products/pdfs/506185a.pdf. The venting section starts on page 7.