I am working on an American Standard furnace that will not cycle off & on. It works only in the "On" position but the air conditioner cycles on & off fine. I have already replaced the thermostat.

Can someone tell me what the problem may be?

bitters
Sep 13, 2014, 02:50 PM
What's model number of the furnace?

RJackson4016
Sep 20, 2014, 03:59 PM
My model # is TWGO25A140B1

bitters
Sep 21, 2014, 11:23 AM
Take the stat off and move G wire to Y terminal, so you have two wires on Y and see what happens. Turn power off to furnace.

I can't find anything on that model #.

RJackson4016
Sep 21, 2014, 02:07 PM
Thanks for the response. I turned off power to furnace and moved G wire to Y terminal, turned power back on to furnace and tried to cycle it on. Nothing.

bitters
Sep 21, 2014, 03:57 PM
Did the AC come on? But no fan?

RJackson4016
Sep 21, 2014, 06:29 PM
Did not hear the AC kick on-definitely no fan. The AC cycles on and off normally. But the heat works only when on ON and not when on AUTO.

bitters
Sep 22, 2014, 06:16 AM
Can you double check the model #? What brand is the furnace? The model number should be inside the top panel (burner compartment) of the furnace.

RJackson4016
Sep 22, 2014, 06:43 PM
American Standard TWG025A140B1 I don't know if the 0's are O's or vise-versa.

bitters
Sep 23, 2014, 09:12 AM
There is very limited info about your furnace on the net. Does the furnace have electric heat coils? If so it could have a bad sequencer. Can you post a close up pic of the wiring diagram?

RJackson4016
Sep 24, 2014, 04:36 PM
Appreciate your help bitters! The furnace have electric heat coils. I hope you can read these diagrams. 46608 46609

bitters
Sep 25, 2014, 09:17 AM
Appreciate your help bitters! The furnace have electric heat coils. I hope you can read these diagrams. 46608 46609

I can't open your attachments. Still would like to see them.

parttime
Sep 25, 2014, 09:21 AM
Rjackson, this link will show you how to post a picture, I hope it helps. https://www.askmehelpdesk.com/support/we-new-sticky-posting-pictures-783127.html

RJackson4016
Sep 25, 2014, 05:47 PM
Thanks parttime! Try this bitters. (Attached below)

bitters
Sep 26, 2014, 09:08 AM
Thanks for the drawings. I don't see see anything in there that would be causing the problem. If you have a voltmeter, set the stat to cool and fan to auto. Then go to the furnace and put your meter on B and T on the circuit board. Make sure the door switch is engaged. If you have 0 volts something is going on in the stat. If you have 24 volts then the circuit board has a problem.

RJackson4016
Sep 26, 2014, 05:36 PM
Okay. I have a meter and will do that, but I have replaced the stat so it's fairly new.

RJackson4016
Oct 7, 2014, 05:45 PM
Hi bitters. I realized the wire diagrams I sent to you earlier were the wrong ones. This diagram is from the "Heater Control Box" and maybe it might help you with my problem. Thanks again.

Grady White
Oct 7, 2014, 06:19 PM
The diagram is no where near complete. We need to be able to see the whole thing.

hkstroud
Oct 7, 2014, 06:45 PM
Are you still working on the furnace problem where you said the heat would not come on when the switch on the thermostat was set to "ON"

RJackson4016
Oct 9, 2014, 05:40 PM
Yes-I'm thinking about searching for the relay or sequencer online as a process of elimination, hoping that will solve the problem.

bitters
Oct 10, 2014, 06:55 AM
Really can't tell anything from the diagram, too big.