LONG STORY: I live in a single-wide from ~1968. We moved out for a few years, and when we moved back in the water heated didn't work any more. The original plumbing was polybutylene. I had tons of problems with it, leaks everywhere, and decided to replace the entire system, since it's only a couple sinks, a tub, and a toilet. So I've replaced the entire system with PVC and CPVC, put a new element in the water heater, and still don't have hot water. I've checked the thermostat and it seems perfectly fine, I get 240v all the way across it, from both sides to the element. The element is band new, never had power to it until water was flowing from the hot side of the sink.
SHORT STORY: Water heater isn't working. It's old and has a brand new element. The cold comes in at the bottom on the side, hot goes out on the top on the side. Nothing on top. Thermostat and element check out perfect, and getting 240v to it
That was the general impression that I got.
Here is my hypothesis. One half of one of your main breakers is either tripped off or is defective. That breaker could be the one in your breaker box, the one in the disconnect on the pole or the breaker in the transformer. It could be tripped from over load, voltage spike or lightening strike during the time the house was unoccupied.
Normally this would show up as the half of your lights and appliances not working. But the side that is working is back feeding through the water heater and any other 240 appliance that is on but not working and is energizing the other side of the panel.
Do voltage check of incoming line lugs with main breaker off. If my hypothesis is correct you will get 120 volts to ground on each lug and 240 across lugs if it is the main breaker in breaker panel. You will get 120 to ground on one lug and 0 on the other lug if it is the breaker in disconnect or transformer breaker.
If you did the voltage check with main breaker in breaker panel on and the breaker in disconnect is at fault, you are getting reading that is a back circuit through water heater. That would explain the 6 volt difference. The 6 volts being the voltage drop across the heating element.
If you get 240 volts across main lugs and get 6 volts across the terminals of water heater breaker, then water heater breaker is faulty. Confirm that by removing breaker and doing voltage check between buss bar contacts.
I'll have to do it tomorrow when it's light out. There are no street lights or anything out here so it's way too dark to safely do anything with the main off at night. Plus my 4 year old would freak out. I'm going to do this first thing tomorrow and report back. Thanks by the way for all your help so far
Sorry for the multiple posts but I'm pretty certain I've found the problem. At the pole the main 100a breaker reads 120v to ground on each side, AND reads 250v across L1 and L2. The buss bar though, only half the poles are hot. So it's like you said, one side is bad, but the power is back feeding through to the house. The problem has to be the main breaker. I checked the bolts where it hooks to the buss bar and the same thing, one side reads 240 and the other reads 0 (with the breakers on).
Only problem now is that the main is tied in to the transformer, so I'm going to have to get the power company to come shut off the power for a few minutes so I can change out the breaker
SHORT STORY: Water heater isn't working. It's old and has a brand new element. The cold comes in at the bottom on the side, hot goes out on the top on the side. Nothing on top. Thermostat and element check out perfect, and getting 240v to it
That was the general impression that I got.
Here is my hypothesis. One half of one of your main breakers is either tripped off or is defective. That breaker could be the one in your breaker box, the one in the disconnect on the pole or the breaker in the transformer. It could be tripped from over load, voltage spike or lightening strike during the time the house was unoccupied.
Normally this would show up as the half of your lights and appliances not working. But the side that is working is back feeding through the water heater and any other 240 appliance that is on but not working and is energizing the other side of the panel.
Do voltage check of incoming line lugs with main breaker off. If my hypothesis is correct you will get 120 volts to ground on each lug and 240 across lugs if it is the main breaker in breaker panel. You will get 120 to ground on one lug and 0 on the other lug if it is the breaker in disconnect or transformer breaker.
If you did the voltage check with main breaker in breaker panel on and the breaker in disconnect is at fault, you are getting reading that is a back circuit through water heater. That would explain the 6 volt difference. The 6 volts being the voltage drop across the heating element.
If you get 240 volts across main lugs and get 6 volts across the terminals of water heater breaker, then water heater breaker is faulty. Confirm that by removing breaker and doing voltage check between buss bar contacts.
I'll have to do it tomorrow when it's light out. There are no street lights or anything out here so it's way too dark to safely do anything with the main off at night. Plus my 4 year old would freak out. I'm going to do this first thing tomorrow and report back. Thanks by the way for all your help so far
Sorry for the multiple posts but I'm pretty certain I've found the problem. At the pole the main 100a breaker reads 120v to ground on each side, AND reads 250v across L1 and L2. The buss bar though, only half the poles are hot. So it's like you said, one side is bad, but the power is back feeding through to the house. The problem has to be the main breaker. I checked the bolts where it hooks to the buss bar and the same thing, one side reads 240 and the other reads 0 (with the breakers on).
Only problem now is that the main is tied in to the transformer, so I'm going to have to get the power company to come shut off the power for a few minutes so I can change out the breaker