PDA

View Full Version : Thermostat, maple chase 2006


Denlinger
Nov 1, 2013, 09:49 PM
My heat pump kicked on the other morning and then just shut off. The thermostat has no display anymore. I went and checked 3 breakers in the box 2 that are listed for the furnace 1 listed for heat pump. All breakers seem on. I also went up in the attic where furnace is and checked those breakers. I hit the resset button in the thermostat.I Also checked the fuse in the thermostat. Nothing seems to work. Wondering if I need to replace the thermostat. Just one other thing I did have my annual service about a month like I have since I moved in.

Grady White
Nov 4, 2013, 05:44 PM
Remove the thermostat & check for 24 volts A/C between R & each other terminal. If voltage is detected, your stat is bad.

Denlinger
Nov 4, 2013, 06:13 PM
Remove the thermostat & check for 24 volts A/C between R & each other terminal. If voltage is detected, your stat is bad.

I checked for volts in stat. No power. But when I was up checking fuse in furnace last night I noticed one of the 60 amp breakers had melted wire coating and looks like the breaker took heat as well. I have service coming in the morning. Hoping its nothing major. Thanks for you help, and taking time out of your day !

Grady White
Nov 4, 2013, 07:23 PM
Sounds like you had a loose connection at the breaker. Did you notice if it was aluminum wire? If it is, every manufacturer I know of says "copper conductors only". I can't tell you how many breakers I've replaced due to the use of aluminum wire.