I have a receptacle that is the only thing on that circuit. Taking out the one fuse kills the power to both outlets. The house was built late 70's When I opened the receptacle up there are 2 main cables. One is a 2 wire the other a 3. The 2 black wires from each cable are attached to each other with a wire nut but are not attached to anything else. The red wire is attached to one side of the receptacle The white white wires are attached to 1 screw each one the other side of the receptacle . The tab is not broken off and there is no wall switch. How do I hook up my new cable to add an receptacle to this circuit?

donf
Aug 3, 2013, 05:33 AM
What you are describing certainly sounds like a switch loop. Question, are the receptacles hot all the time?

The source (Black) is connected to the switch supply (Black). The Neutral (White) is carried to the switch outlet for use by a specialty device (Motion Detector), and then the power is returned to the receptacle via the Red conductor.

The unbroken tab on the receptacle just means that whatever means controls the return power to the receptacle makes both receptacles on the yoke hot. Sometimes the design of the circuit would call for a double receptacle (two receptacles on one yoke) one would be a constant hot while the other would be controlled by a switch. In that situation, the tab would be broken and you would see a black conductor and a red conductor connected to the receptacles.

Tmack485
Aug 3, 2013, 06:42 AM
What you are describing certainly sounds like a switch loop. Question, are the receptacles hot all the time?

The source (Black) is connected to the switch supply (Black). The Neutral (White) is carried to the switch outlet for use by a specialty device (Motion Detector), and then the power is returned to the receptacle via the Red conductor.

The unbroken tab on the receptacle just means that whatever means controls the return power to the receptacle makes both receptacles on the yoke hot. Sometimes the design of the circuit would call for a double receptacle (two receptacles on one yoke) one would be a constant hot while the other would be controlled by a switch. In that situation, the tab would be broken and you would see a black conductor and a red conductor connected to the receptacles.
Yes both outlets are hot all the time and there is no switch to operate the outlet.

hkstroud
Aug 3, 2013, 07:20 AM
I have a receptacle that is the only thing on that circuit. Taking out the one fuse kills the power to both outlets.

Those two statements are logically inconsistent.

Sounds like, at least initially from your description of the wiring, that you have two circuits sharing a neutral.

ma0641
Aug 3, 2013, 08:31 AM
Agree with Harold, the red and black wire are a typical tell tale. Probably a 14 or 12/3 wire. At the fuse box, are both red and black under the connector? Usually there will be 2 fuses or breakers today. If this is a kitchen, you should have GFCI's but they will not function on a shared neutral.

Tmack485
Aug 3, 2013, 08:51 AM
Those two statements are logically inconsistent.

Sounds like, at least initially from your description of the wiring, that you have two circuits sharing a neutral.
Referring to the outlets on the one receptacle. So can I add a receptacle ?

ma0641
Aug 3, 2013, 09:01 AM
Although you can extend wiring on a shared neutral, it is not recommended because it unbalances the circuit. Depending on upstream usage and wiring done by a previous installer, the downstream neutral can be hot, please read the following, copied from one of my electrical books.
"In the interest of safety and protection of equipment, all 120 volt branch circuits that extend beyond a distribution panel board should be complete and independent of any other branch circuit. This means that all 120 volt circuits should have dedicated neutrals, and that shared neutrals should not be employed to feed receptacle circuits. In addition, these dedicated neutrals should be identified with the corresponding circuit number, at every splice. In this way, the electrician that comes to alter or extend and existing circuit, is less likely to tap the wrong neutral".

donf
Aug 3, 2013, 09:12 AM
While agree that 3 conductor could easily be associated with a multi-wire circuit I disagree in this instance because:

There would be two breakers associated with the multiwire circuit. There is no suggestion at all that there is a breaker with a red conductor.

What the poster is describing is a two conductor feed from the source, connecting with a 3 conductor cable. To me this is indicative of a switch loop.

Why would any electrician use a 3 conductor cable to share a neutral on the same single circuit breaker?

What you are describing doesn't make sense. Since there is no connected source (that we know of at this time) on the Red conductor? Where is the power coming from? We do know that black is feeding something else on the circuit and that red is receiving power from somewhere else on this circuit.

Stratmando
Aug 3, 2013, 09:25 AM
Despite what I am reading, I don't see why you can't connect to the red and white(and a ground), You must pigtail the white, receptacle terminals cannot be used to complete Neutral.
If a Multi Circuit, it should be on a 2 pole breaker, so it turns off both circuits at once, An open neutral on a multicircuit can provide volatges anywhere from 1 to 239 volts, and cause serious damage.
I would determine what that black wire goes to.
Safely expose wirenut to allow testing to determine which breaker.
Am not for sure if you mean 2 duplex recepticles or 1 Device?
The Neutral on a Multi Circuit carries the difference of the 2 hots(If 1 circuit draws 15 amps, and the other draws 20 amps, The neutrals load would be 5 amps).
Good Luck

IMPORTANT, Power MUST be off on both circuits, especially when dealing with the Neutral.

donf
Aug 3, 2013, 09:42 AM
Here is a simple test.

With the circuit breaker in the OFF position, sepaeate the two black conductors and then cap off the black conductor from the breaker.

If this is a true multi wire circuit, then the receptacle will still becaues it beingf fed by its own breaker.

I the receptacle goes dead, then there is a device that is controlling power to that receotacle.

Is this receptacle near the entry to a room? If it is, look for a wall switch on any outside wall near the room. For example, in the hallway near the entry door.

Something is controlling the feed to the recptacle if that receptacle goes dead with the black conductors separated.

Tmack485
Aug 3, 2013, 10:14 AM
Here is a simple test.

With the circuit breaker in the OFF position, sepaeate the two black conductors and then cap off the black conductor from the breaker.

If this is a true multi wire circuit, then the receptacle will still becaues it beingf fed by its own breaker.

I the receptacle goes dead, then there is a device that is controlling power to that receotacle.

Is this receptacle near the entry to a room? If it is, look for a wall switch on any outside wall near the room. For example, in the hallway near the entry door.

something is controlling the feed to the recptacle if that receptacle goes dead with the black conductors separated.
New information one of the black wires is powering the fridge outlet. I assume this means I have multi branch wiring. Does the fridge receptacle count towards the load on the circuit from the receptacle I want to tap into? I unscrew another fuse to shut power off to the fridge.

hkstroud
Aug 3, 2013, 10:30 AM
OK, so you have a duplex receptical, two outlets on one yoke.

Your wiring indicates that there is something else on the circuit.

That something else could be outlets or lights. Turn off breaker, do a voltage test on both the black and the red wire.

If power is coming in on the 3-wire cable then you have two circuits sharing a neutral.
If power is coming in on the 2-wire cable then logic says that this is a switched outlet. The white of the 3-wire e cable is neutral of course. The black takes power to the switch and beyond. The red of the 3-wire returns power to the outlet from the switch. The tab on the hot side of the outlet is removed if only one half of the outlet is switched and the other half is constant hot.

If can think of no other reason for using 3-wire cable out of an outlet box other than a switched outlet and also a need for power beyond the switch the switch location.

Edit after your latest post.


New information one of the black wires is powering the fridge outlet.

I unscrew another fuse to shut power off to the fridge.

That indicates two circuits sharing a neutral. Power should be coming in on the 3-wire.

hkstroud
Aug 3, 2013, 10:39 AM
Can you add an outlet?

Yes.

Connect the two existing white wires together and add a pigtail. Connect the pigtail to the neutral side of the outlet. Connect the white of cable going to new outlet to neutral side. Connect black of cable going to new outlet to hot side of this outlet.

Tmack485
Aug 3, 2013, 10:57 AM
Can you add an outlet?

Yes.

Connect the two existing white wires together and add a pigtail. Connect the pigtail to the neutral side of the outlet. Connect the white of cable going to new outlet to neutral side. Connect black of cable going to new outlet to hot side of this outlet.

Thank you. One final question I hope. Can I add a gfci receptacle to the new receptacle I want to put in? In other words there would be 3 receptacles and the gfci would be the last one.

donf
Aug 3, 2013, 12:19 PM
Certainly you can, but GFCI receptacles are primarily for use near water, kitchens, bathrooms, basements garages and outdoors.

Depending on the room you may have to install an AFCI receptacle, not a GFCI receptacle.

Tmack485
Aug 3, 2013, 12:36 PM
Certainly you can, but GFCI receptacles are primarily for use near water, kitchens, bathrooms, basements garages and outdoors.

Depending on the room you may have to install an AFCI receptacle, not a GFCI receptacle.
This would be in the bathroom. There was one in there wired to the light with the wire running on top of 2 studs and I almost put a screw through the wire so I got rid of that and just want to run a wire properly. The other receptacle is in the room next the bathroom so just an ordinary receptacle.

donf
Aug 3, 2013, 04:02 PM
Stop right there!

You cannot feed a receptacle in a bathroom with a general use circuit.

NEC allows for a 20 amp circuit to feed multiple bathroom room receptacles, but the circuit is for bathrooms only. You cannot connect to a circuit that supply's any other devices. Only bathroom receptacles.

hkstroud
Aug 3, 2013, 05:32 PM
Present codes require a dedicated 20 amp circuit to a bath. If you have screw in fuses you are certainly not under present or recent codes.

Code does not prohibit additional circuits (or outlets) to bath.

donf
Aug 4, 2013, 05:13 AM
Again, I have to disagree with the previous statement.

Just because a home has a fuse box instead of a breaker box does not correlate to the level of code. This home was built in the 1970s, that correlates to the level of code.

There is no prohibition against the use of a fuse box that I can find in either the 2008 or 2011 editions of the NEC.

So the real question is when did code begin requiring a 20 amp dedicated receptacle branch circuit for a bathroom or bath rooms. Also, would the AHJ allow the use of an extension of a 15 amp general use branch circuit to include the use of a 15 amp branch circuit .

The use of a hair dryer on a 15 amp circuit is risky enough to trip the circuit (overload) so why risk it?

Current code allows the use of 1 dedicated 20 amp branch circuit for one entire bathroom or the use of one dedicated 20 amp branch circuit for receptacles only in more than one bathroom.

Stratmando
Aug 4, 2013, 08:02 AM
Tripping an addition outlet on different circuit would not leave you in the dark.
Better the additional circuit trip, than the Lighting, Leaving you in the dark and dangerous?
Opinion, nothing to do with code?
Would leave the frige alone on the black circuit.

hkstroud
Aug 4, 2013, 09:29 AM
Current code allows the use of 1 dedicated 20 amp branch circuit for one entire bathroom or the use of one dedicated 20 amp branch circuit for receptacles only in more than one bathroom.

That would be a minimum. Does not prohibit additional circuits regardless of the code the house is under. Additional circuits would not have to meet restriction of "bath only".

donf
Aug 4, 2013, 02:27 PM
Hank,

I know I seem to acting like a PIA on this thread but that is not my intent, in any way.

While the current code states that a min. of one dedicated 20 circuit is required for an entire single bathroom (inclusive of the receptacles) or a single dedicated 20 amp circuit for receptacle use only in more than one bathroom is all that is required.

I read that to mean that if I want to add more branch circuits that's fine as long as they are dedicated branch-circuits and they are 20 amp.

Am I being semi-brain dead on this or splitting hairs to finely?

Don

hkstroud
Aug 4, 2013, 02:39 PM
Don
If your wife told you that you had to have $20 in your wallet when you left the house, and that you could only use that $20 for gas. That wouldn't mean that you couldn't have another $15 for a hamburger. And you wouldn't have to spend that $15 in one place. You could stop and buy her flowers on the way home from the burger joint.

You have met the requirement of having $20 for gas.

parttime
Aug 4, 2013, 02:46 PM
This thread makes me wonder what ever happened to TKRussel?

donf
Aug 4, 2013, 02:49 PM
Well, I'm not sure that my Lady would allow that much currency in my wallet at any one time. My Lady is Scottish / Italian, she hails from a suburb of NYC (New Rochelle) and she was a U.S. Marine. I don't even try to pick a fight. I'm just an NYC kid from the Bronx that wisely chose the U.S. Navy. :)

I'm not saying that there can't be a 15 amp line for run into the bathroom for other purposes than a receptacle outlet.

I'm saying that if a circuit is run to a bathroom to supply a receptacle outlet, it is required to 20 amp. It cannot sit on the end of a 15 amp extended branch circuit. The focus I'm using is on the receptacle outlet, not a circuit that may supply lighting or other general use devices.

hkstroud
Aug 4, 2013, 04:24 PM
I'm saying that if a circuit is run to a bathroom to supply a receptacle outlet, it is required to 20 amp.
Why would you say that. Present and recent codes require a 20 amp circuit to a bath, serving only that bath or another bath. That does not prevent a second circuit from also serving that bath.
Just think of that second circuit as being a general lighting circuit.

While we don't know what code this structure comes under, the fact that the distribution panel uses fuses rather than breakers, is a good indication that the code probably predates the requirement that there be a dedicated circuit to the bath. I know of no requirement that all circuits to a bath be dedicated or that they must be 20 amp.

A general lighting circuit does not mean light fixtures only.

donf
Aug 4, 2013, 08:27 PM
Harold,

I cannot about code editions prior to the 2008 edition. I do have a copy of the 2005 edition but that is all the way across my office and I'm just to lazy right now.

The code a minimum of 1 20 amp branch circuit to serve a bathroom, inclusive of a GFCI receptacle outlet. Yes, there can be more than one circuit. However, if there is only the one 20 amp circuit, it is not permissible to serve any other bathroom.

If there is a dedicated 20 amp circuit for the exclusive use of the receptacle outlet then you have the option to extend that circuit to another bathroom for the exclusive use of a receptacle outlet. It cannot serve any other loads but receptacles.

Are we saying the same thing?

Tmack485
Aug 5, 2013, 01:38 AM
Harold,

I cannot about code editions prior to the 2008 edition. I do have a copy of the 2005 edition but that is all the way across my office and I'm just to lazy right now.

The code a minimum of 1 20 amp branch circuit to serve a bathroom, inclusive of a GFCI receptacle outlet. Yes, there can be more than one circuit. However, if there is only the one 20 amp circuit, it is not permissible to serve any other bathroom.

If there is a dedicated 20 amp circuit for the exclusive use of the receptacle outlet then you have the option to extend that circuit to another bathroom for the exclusive use of a receptacle outlet. It cannot serve any other loads but receptacles.

Are we saying the same thing?

I think the codes a little different up here in Canada. What I've found for code there's no mention about needing a separate 20 amp circuit in a bathroom just a gfci. Could be wrong though.

donf
Aug 5, 2013, 11:52 AM
Well, I am basing my responses on the 2011 edition of the NEC. Chapter 2, citations 210.11(C)(3) and 210.52(D).