My hvac blower motor works in heat mode only not cooling, will not work with manual mode either

Joshdta
Jul 23, 2013, 04:20 PM
Not knowing what brand unit you have it is either fan relay or the control board is bad

Grady White
Jul 25, 2013, 07:05 PM
With the little information given, I would have to suspect either a bad fan motor or fan relay. The relay could be on a board or separate. Another possibility is a bad thermostat or thermostat wiring. The 'G' terminal on the stat & the wire between it and the furnace are the source of the control for the fan in cooling & manual fan. If 24 volts is not getting back to the 'G' terminal on the furnace the fan won't run in cooling or manual fan.