I have a Carrier Weathermaker 8000 furnace (58WAV090-JC) with a Lennox condenser (HS26-042-2P). When I turn the A/C on at the thermostat, the blower in the furnace turns on but the condenser unit outside does not. I have taken the following troubleshooting steps:
1. Check contactors inside condenser unit: I get 240 volts to the contactors, nothing out the other side. When I push the contactors in manually, the compressor and fan turn on. I checked the low voltage terminals on either side of the contactor switch, and got no voltage reading. Conclusion: Compressor and fan work, but the contactor is not getting the signal from the thermostat/furnace to turn on.
2. Check the wires coming out of the thermostat: Put my volt meter on the red and yellow wires. With the thermostat set to off, I get 25V. Turn the thermostat on, I get 0 Volts. Conclusion: Thermostat is working properly.
3. Check control circuit board inside furnace: The red wire coming from the thermostat connects to the "R" terminal, and the yellow wire connects to the "Y" terminal. Putting my volt meter on the R and Y terminals, I get 25V with the thermostat off and 0 Volts with the thermostat on. Conclusion: Connection from thermostat into control board is good.
The wire going out to the outside condenser unit connects to the "C" and "Y" terminals. Putting my voltmeter on these, I get the opposite as above--thermostat off = 0 Volts, thermostat on = 24 V.
Conclusion: something in the control board is bad. Fix: replace control board.
Before I go out and spend a couple hundred on a new board, am I doing this right? Does my troubleshooting sound correct?
1. Check contactors inside condenser unit: I get 240 volts to the contactors, nothing out the other side. When I push the contactors in manually, the compressor and fan turn on. I checked the low voltage terminals on either side of the contactor switch, and got no voltage reading. Conclusion: Compressor and fan work, but the contactor is not getting the signal from the thermostat/furnace to turn on.
2. Check the wires coming out of the thermostat: Put my volt meter on the red and yellow wires. With the thermostat set to off, I get 25V. Turn the thermostat on, I get 0 Volts. Conclusion: Thermostat is working properly.
3. Check control circuit board inside furnace: The red wire coming from the thermostat connects to the "R" terminal, and the yellow wire connects to the "Y" terminal. Putting my volt meter on the R and Y terminals, I get 25V with the thermostat off and 0 Volts with the thermostat on. Conclusion: Connection from thermostat into control board is good.
The wire going out to the outside condenser unit connects to the "C" and "Y" terminals. Putting my voltmeter on these, I get the opposite as above--thermostat off = 0 Volts, thermostat on = 24 V.
Conclusion: something in the control board is bad. Fix: replace control board.