View Full Version : Compressor icing up


136Serenity
Mar 12, 2013, 12:55 PM
My compressor sometimes ices up when the heat runs. Sometimes just on top of the unit, sometimes the coils and on top. We have had the furnace checked and our repairman says everything is working as it should however I have never had a compressor that did this before. Any suggestions?

ma0641
Mar 12, 2013, 01:34 PM
Defrost cycle is as follows.
The defrost control detects the buildup of ice on the outdoor coil. The reversing valve solenoid de-energizes, directing hot gas from the compressor to the outdoor coil to defrost. The outdoor fan stops. If it didn't, cold air from the fan prevents the melting effect of the hot refrigerant. As the temperature of the indoor air drops, controls energize the electric heat elements to warm the indoor air. When the defrost control detects the ice has melted, it terminates the defrost mode. The reversing valve shifts to the heating position and directs hot refrigerant gas to the indoor coil. The outdoor fan operates. The electric elements cycle off.
So, it sounds like either the defrost control or reversing valve is occasionally sticking.

Grady White
Mar 12, 2013, 05:04 PM
What you are experiencing is perfectly normal for a heat pump.

mygirlsdad77
Mar 13, 2013, 05:32 PM
I have to agree with Grady on this one. Completely normal for a heat pump during heating season.

wmproop
Mar 14, 2013, 09:36 AM
I agree with mygirlsdad77,, but not sure about Grady White, :) :)

mygirlsdad77
Mar 14, 2013, 03:19 PM
Yep, wmproop, Grady and I did have completely different opinions.. lol.

wmproop
Mar 14, 2013, 03:48 PM
;)

Grady White
Mar 15, 2013, 09:44 AM
Yep, wmproop, Grady and I did have completely different opinions..lol.

One of us is dead wrong. :)