View Full Version : I have a new honeywell theromostat I just installed and the display won't come on


garrettcox58
Nov 27, 2012, 06:26 PM
Its brand new and I did follow the directions what could I try next to fix it

Grady White
Nov 27, 2012, 07:07 PM
What is the model number of the stat & to which terminals are wires connected?

garrettcox58
Nov 27, 2012, 07:20 PM
Only 4 wires... Green wire is on G... Yellow is on Y red is on RC and white is on W

Grady White
Nov 29, 2012, 07:44 PM
Only 4 wires... Green wire is on G... Yellow is on Y red is on RC and white is on W

Unless the thermostat has batteries, you probably need to run a wire from the common terminal on the furnace to the "C" terminal on the stat. What is the model number of the stat? I need that to look up a wiring diagram.

wmproop
Nov 30, 2012, 05:36 AM
If you didn`t turn off the breaker before install you might have fried the transformer ( hence there is no 24 volts coming to the tstat) with fried transformer