PDA

View Full Version : Where do we locate a arc fault breaker in a residential home?


jack tozzi
Nov 15, 2012, 10:49 AM
The residential code for arc fault breakers ?

tkrussell
Nov 15, 2012, 10:58 AM
Section 210.12 of the 2008 edition of the National Electric Code. Your area may use the 2011 edition.

Can be reviewed at:

NFPA 70: National Electrical CodeŽ (http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=70)

jack tozzi
Nov 15, 2012, 11:01 AM
After running 14\3 romex wire arc fault breaker will not stay on please help

jack tozzi
Nov 15, 2012, 11:06 AM
Why can't I install a gfic outlet on load side to replace arc fault breakers

hfcarson
Nov 15, 2012, 11:16 AM
First, they are different devices and protect against different conditions...
If you want to remain code compliant you cannot replace one with the other.
Why would you want to do this?

hfcarson
Nov 15, 2012, 11:18 AM
Tell us more...
Is this circuit inside your house? What is connected to it? Does this circuit
Feed a receptacle? Describe the situation better...

donf
Nov 15, 2012, 11:26 AM
Please only open one thread at a time.

How old is the residence that this circuit is in? Why are you installing an Arc Fault breaker in the first place? Did you just install a new circuit or panelboard.

An Arc Fault trips when it sees the signiture of an arc. Its purpose is to prevent fires so two conclusions are possible from the little you describe. There is in fact an arcing condition being dected. The breaker is bad.

Give us more to go one and maybe we can help you out.

donf
Nov 15, 2012, 11:31 AM
Okay, not the to be a smart a$$ but breakers are installed in panelboards. Was that a trick question? :)

jack tozzi
Nov 15, 2012, 11:41 AM
First, they are different devices and protect against different conditions...
If you want to remain code compliant you cannot replace one with the other.
Why would you want to do this?

After running 14\3 romex wire the arc fault needs its own neutral to each circuit how can I correct this after sheetrock

jack tozzi
Nov 15, 2012, 11:56 AM
Tell us more...
Is this circuit inside your house? What is connected to it? Does this circuit
feed a receptacle? Describe the situation better...
This 14\3 circuits are ran to a wall outlet and then split one going to overhead cans and other to closet and wall outlets in master room keep in mind the can light circuit also hits a few wall outlets that need to be arc fault stupid please help thanks

jack tozzi
Nov 15, 2012, 12:12 PM
After running 14-3 romex wire to an outlet and splitting one to overhead can lighting and the other to master bedroom outlets. Keep in mind, that can lighting circuit also hits two wall outlets also. They also need to be arc fault stupid. Please Help.

Curlyben
Nov 15, 2012, 01:00 PM
>Numerous Threads Merged<

donf
Nov 15, 2012, 02:54 PM
Curly,

I just noticed that this post was originally opened in 2007. Jack, would you please consider opening a new post for your questions.

Thank you.