Sep 10, 2012, 07:26 AM
We have a fabrication shop and I need to run 5 more single phase 230 plug ins for our welders. How do I go about this?
ma0641
Sep 10, 2012, 08:13 AM
Do you have the amperage capacity for this number of welders? You need to do a load determination vs. wire ampacity and if acceptable, add the additional outlets. Or, you may need a new service for the welders. We know nothing about your welders, Stick, TIG, MIG?? Get the info from the plates on the welders.
shuntripper
Sep 16, 2012, 09:02 AM
Standard plug that comes on many welders is Nema 6-50P, receptacle is 6-50R. As long as you have 8 unused CB spaces in a panel, they will each come from one two pole 50A CB. Your main will trip at this panel if you exceed it's amperage rating though.
Do you have single phase or 3 phase power at the panel? If you have 3 phase do you know if you have a high leg in that panel? What is the main/disconnect amperage rating for that panel? Is the panel fed from a transformer?