What is the nfpa on warehouse lighting

hfcarson
Jul 2, 2012, 08:41 AM
Please explain your question in more detail...
For typical warehouse lighting the NFPA has no requirements. Any requirements
Would come first from the Building Code with possible recommendation from the IESNA.

tkrussell
Jul 3, 2012, 10:35 AM
The only reference in NFPA 70 regarding lighting is to allow for .25 VA per square foot as a minimum load of general lighting, and to use the first 12,500 VA at 100% when doing load calculations.

If you would answer Hfcarson's question and provide more detail, perhaps we can provide a better answer.