0qwerty
Jun 21, 2012, 10:52 AM
I have a Goodman Split Unit Heat Pump that has a chattering Contactor. It is only getting 18 volts to the Contactor, but when you disconnect it, the voltage rises to 28 volts. I have put several Contactors of different brands on it with the same results.
Any suggestions?

hvac1000
Jun 21, 2012, 11:38 AM
I have a Goodman Split Unit Heat Pump that has a chattering Contactor. It is only getting 18 volts to the Contactor, but when you disconnect it, the voltage rises to 28 volts. I have put several Contactors of different brands on it with the same results.
Any suggestions?

Could be a weak transformer, It might show voltage but not enough milliamps/VA. Use a minimum of 40 VA for the transformer. Now loose low voltage wiring can cause this and I have seen thermostats cause this problem also. Good luck.