View Full Version : Sub panel question


Kyle_in_rure
Jan 21, 2012, 03:50 PM
I was thinking of running a 60 amp sub panel to a barn about 75 feet from the main panel. I've read that in a sub panel ground and neutral must be separated. However, can I just run three wires (hot, hot, neutral) to the barn, and drive a grounding rod at the sub panel, and leave the ground and neutral bonded in the subpanel? Thanks

tkrussell
Jan 22, 2012, 04:46 AM
No, the new feeder must be 4 wire, with two hots, one insulated neutral and one insulated equipment ground conductor.

The three wire method is no longer allowed.

Kyle_in_rure
Jan 22, 2012, 11:13 AM
Is there a particular reason this is no longer allowed?

tkrussell
Jan 23, 2012, 03:31 AM
4 wire system is safer than 3 wire.