View Full Version : I need to go from 480v. To 208v. Using a stepdown transformer to get 200amps ?
soupy909
Dec 19, 2011, 03:45 AM
I need to get from 480 to 208 and need 200amps what size transformer do I need?
Stratmando
Dec 19, 2011, 06:11 AM
480 X 200 = 96,000 Watts(VA)
I would wait for an answer from TK, Stanforty, or Missouri, or other qualified.
tkrussell
Dec 19, 2011, 07:20 AM
200 Amps x 208 volts x 1.73 = 71.968 KVA
You need a standard size 75 KVA transformer.
Check with your supplier for pricing and what the customer needs are, may need isolation, K rated, Low Temp, etc.
Do need to consider, is the total connected load 200 amps?
Can load a transformer 80% of nameplate rating.
Since your dealing with 480 volts, I assume you're an electrician and know all the rules regarding transformers, feeder rating, etc.
soupy909
Dec 20, 2011, 02:32 AM
Thanks tkrussell
tkrussell
Dec 20, 2011, 07:13 AM
Your welcome, Soupy,but you did not answer my questions about calculated load and your qualifications.
By the way, my calculation includes a shortcut I did not show.
The actual formula is: KVA=I x E x 1.73/1000
Using your values:
KVA = 200 Amps times 208 Volts x 1.73 (assuming 3 phase) and divide by 1000 will result in 71.968 KVA
You can see this and other useful power formulas here:
Useful Formulas (http://www.elec-toolbox.com/Formulas/Useful/formulas.htm)