View Full Version : 220 Outlets & GFCI Questions
JimV
Feb 6, 2007, 08:59 AM
I'm wanting to add some 220 outlets in the garage to run my woodworking equipment, and I have a couple of questions. First, can I run one 220 circuit with approximately 4 plugins on it? Only 1 piece of equipment will ever be used at one time (or does this violate code? ). Also, I'm under the assumption that since it's in a garage (attached) even the 220 circuits must be GFCI. Do I have to install GFCI breakers in my subpanel, or is there such a thing as a GFCI plugin for 220? Thanks for your help.
Jim
tkrussell
Feb 6, 2007, 11:18 AM
Sure, 4- 240 volt receptacles can be on one circuit.
Code only requires 120 volt receptacles in a garage to be GFI protected.
However, having a 240 volt circuit in a garage for the purpose of a power tool would be a good idea, and the only way to do this would be to use a 2 pole 240 volt GFI circuit breaker.
JimV
Feb 7, 2007, 01:06 PM
Thanks! Now if you could help me understand one other thing. I've looked over the three tools that will be run on the 240 volt circuit (again, only one at a time) and the one with the largest draw is the table saw (3hp, 220V, 18A). With that in mind how do I figure out the proper sized breaker and wire to complete this circuit? Thanks again.
Jim
tkrussell
Feb 8, 2007, 12:40 PM
Branch circuit size is rated 125% of the running load of a motor, 18 x 1.25=22.5 amps, so the wire must be at least #10 with a 25 amp breaker. A 30 amp breaker is allowed also.