Jul 15, 2011, 01:52 PM
Changing service disconnect. Service cable (1/0 aluminum) underground service is short by 2 ft for termination in new disconnect. Is it code compliant to splice (compress,butt) #1 copper(thhn)?

donf
Jul 15, 2011, 04:33 PM
Please be a little clearer.

What service are you changing?

Are you talking about the conductors from the transformer to disconnect? Or from the disconnect to main service panelboard?

chuckr97
Jul 15, 2011, 04:44 PM
Changinging main serice disconnect. Conductors from xformer to disconnect (combo)

donf
Jul 15, 2011, 05:36 PM
If those conductors are connected to a Power Company transformer then they are the property of the Power Company, why are you changing them? You need their permission to touch those feeders.

You do realize that you would be working on live, unprotected conductors that could very easily kill you, don't you.

Fr_Chuck
Jul 15, 2011, 05:43 PM
Yes, at least where I am at, the power company always does those wires. If they need to be changed for new service panel, they will change them out after you replace the house feeds

tkrussell
Jul 16, 2011, 03:28 AM
Don and Fr Chuck, Chuck is not asking about replacing the underground wiring, he is asking about extending the wire.

Chuck, this question I answered and gave you a product to use in this thread :

https://www.askmehelpdesk.com/electrical-lighting/code-compliant-compression-splice-aluminum-feeder-copper-feeder-587496.html


There are pre-insulated mechanical connectors that use wrenches to splice large wire/cable, you are not limited to crimp style.

chuckr97
Jul 16, 2011, 01:41 PM
Thanks for help!