I'm hoping someone can help with this question. We are installing an electric wall furnace, 240 volt, 38 amp, 9.2kwh. I was told by the guy at the hardware store to use size 8 wire. The instructions (?? ) that come with the unit don't sat anywhere what size is to be used! Is size 8 wire correct?
Thanks,
Mel

tkrussell
Jan 25, 2007, 04:10 PM
The wire size needs to be rated not less than 125 % of the nameplate load.

9400 watts / 240 volts = 39.17 x 125%= 48.96 amps

If you use NM-B Romex, then the smallest wire can be #6 copper.

Only if you use MC cable, or pull THHN wire through conduit, then #8 copper THHN can be used.

A 50 amp breaker is needed.

melodygardens
Jan 25, 2007, 07:37 PM
Thanks TKrussell. Wired it up with NM-B Romex #6 copper with 50 amp fuse, and it seems to be working OK. Thanks for the quick response!