Whould somebody tell me how to install the T194R timer to a water bomb 1.5 hP 15amp and another pump 1hp both used for water fall.

Hanks, Vic

tkrussell
Mar 22, 2011, 05:31 AM
Since the title of the question states T104R, is the T194R in the body of your question a typo?

The instruction manual for the T104 has a wiring diagram.

http://www.intermatic.com/~/media/files/intermatic/products/instructions/timers/t104%20-%20english.ashx

This unit has a 240 volt timer motor and is designed to switch a 240 volt load.

Are the two motors you have 240 volts?

Assuming both are on the same circuit, the 1 HP motor at 240 volts is 8 amps, and the 1.5 HP is at 10 amps, totalling 18 amps.

This circuit needs to be a minimum of 30 amp circuit with a 2 pole 30 amp breaker and all #10 copper wire.

If these pumps are for a fountain, or something that peple will enter, the breaker needs to be a Ground Fault device.

What are these pumps for?