Log in

View Full Version : NEC 2011, Section 404.2 - Request for Comments


donf
Feb 19, 2011, 06:43 AM
Greetings,

Talk about "BOHICA" (Navy term for Bend Over Here It Comes Again)

404.2(C) requires that switch outlets be served by a Neutral conductor to make sure that if electronic switches (motion detectors) may be used, the Neutral will be in place. If the outlet is connected via conduit, Neutral is not required because it can be pulled if ever needed.

This means, at least to me, that any switch loops will have to be run using a three wire cable. Neutral will have to be capped off.

Of course the customer will eat the cost increase. Increased use of Copper will drive the cost up. Such a waste of Copper for a "possible" future use. Aluminum may return to keep costs down.

Personally, it would have been better to require conduit runs to switch outlets than waste Copper.

tkrussell
Feb 20, 2011, 05:55 AM
I see the point of the new requirement, to eliminate the lack of a neutral in a switch location for the popular electronic dimmers, timers, occupancy sensors, etc, that require a neutral to operate.

So many people have attempted to install these devices and cannot since a neutral is missing. I wonder how many have been installed using the equipment ground where a neutral was missing.

One person out of 12 of the Code Making Panel voted against this, citing additional cost to wiring a dwelling. The others considered the likelihood of electronic devices being installed as being more possible.

The installer will need to plan the circuitry to be sure a neutral is at each switch location. I do not see this as a serious hardship. Switch loops will go away. Simply bring a feed to a switch then continue onto the load.

Sure there will end up that some neutrals will be installed that are not currently needed. I do not see the added cost being that large.

As an installer, I would have choices, either configure the wiring so the feed goes to a switch location first, or use a three wire cable where I really have my heart set on using a switch loop, or use raceway for my switches that would allow a neutral to be added in the future if needed.

Also note, this requirement is NOT required for any 3 way or 4 way switches, ONLY single pole switches.

I think it is important to note that this proposal came from the National Electrical Manufacturers Association, the group that makes the switch devices, not the Copper industry.

Keep in mind, the issue is Safety, to prevent the practice of using the equipment ground being used as a return, and convenience, to allow these devices to be used when desired.

These are my comments, not saying I am for or against it, just noting the purpose of the requirement and how to deal with it.

Fortunately I do not do residential as part of a business any longer. I would not want to do home wiring considering all of the requirements and the cost.