PDA

View Full Version : Beacon Morris BTU 45 won't ignite


bjrice99
Feb 11, 2011, 02:56 PM
I have a Beacon Morris BTU 45 garage furnace.
When I turn it on it goes through the process of heating with the exception of no heat.The blower starts up to expel any gas, the ignitor lights up and then the main blower comes on.
I put a flame to the burners and nothing happened. It seems like there is no gas getting to the furnace. ANy help?

T-Top
Feb 11, 2011, 08:53 PM
Dirty burners, no gas pressure or a bad gas valve. If you have gas pressure at the IN on the gas valve and nothing on the OUT with 24v going to the valve it's a bad gas valve. You have to use a manometer to make for sure it's a bad gas valve and not a restricted manifold,burner orifice or just dirty burners. Checking inlet and outlet pressures will let you know if you have a bad valve.

Theaircoguy
Feb 11, 2011, 10:47 PM
I agree with T-top. Make sure you have gas going to the gas valve and that if it has a switch, that it is in the on position.