I want to hook up 220 in my garage for a air compressor I just bought, I've ran a 110 line to the garage before for a smaller air compressor, I have 200 amp service panel with plenty of open slots. The air comp has just 3 wires, red, black, and green. Do the breakers go in the same way as the 110v breakers? If somebody could give me the basics I'm sure I can do it,! THANKS, MARK

Missouri Bound
Nov 12, 2010, 08:25 PM
You will use a two pole breaker. The red and black will connect to the breaker, the green is your ground. Read the label on the motor to verify the amperage and choose the wire and breaker accordingly. The breaker goes in exactly like the 120v breakers, except that it takes up two slots in the panel.

donf
Nov 13, 2010, 04:25 PM
If you are in the U.S.A. the voltage is 240.

Question,

Should not the poster get the nameplate amperage off the motor plate and then get the "Full Load Current" out of the tables in Article 430, to correctly size the conductors and required breakers or is this overkill?

fuseman
Nov 13, 2010, 05:51 PM
How many hp is the motor, and how far away will the compressor be from the power or socket.

fuseman
Nov 13, 2010, 05:54 PM
What is the full load amps say on the lable of the motor.

Camaro00440
Nov 13, 2010, 07:33 PM
thanks guys... it's 6.5hp... 15amp... l.r amps = 93... output 298kw... this is what's on the motor

Missouri Bound
Nov 13, 2010, 08:23 PM
Use a 20 amp breaker for that... 12 ga. Wire.

Camaro00440
Nov 14, 2010, 09:13 AM
I bought 10gauge wire, the compressor is about 25 ft away from the breaker panel, and a 20amp breaker, is this OK? Over kill. Or not enough ? Going to put a plug on it because I want to plug in a 220 welder too!

Missouri Bound
Nov 14, 2010, 12:39 PM
It's absolutely fine. It will also allow you to move up to a 30 amp breaker should your needs change.

fuseman
Nov 15, 2010, 08:45 PM
Hook the compressor up,and plug and wire 25' is long enough,let us know how its going.

Missouri Bound
Nov 15, 2010, 08:58 PM
Now I'm confused. Are you running a circuit for the compressor using 10/3 wire, or are you putting a 10/3 wire on the compressor with a plug on the end of it? Not quite the same. Fuseman's last post has me wondering exactly what it is you are doing, and could definitely change the advice given.

Camaro00440
Nov 16, 2010, 03:21 PM
OK, I'm running 10/2 wire ( red, black, green) from the breaker panel, 25ft into the garage (attached) to a plug in the wall, then 10/2 wire from the compressor to the plug, about 5ft, (20amp breaker in the panel ) I'm using a plug so I can plug in a 220v wire welder also!! (when compressor's not plugged in)