PDA

View Full Version : York board flashing 5 times


bm11027
Nov 1, 2010, 06:43 AM
My York AC/Gas pack unit circuit board red led is flashing 5 times. The inducer motor and blower motor continuously run even when I switch to the AC mode. I am not getting any heat or AC. Please help. I have changed the thermostat but no resolution. Model is: D3GA036N07006A.

bm11027
Nov 9, 2010, 05:20 AM